If not specified in the manuf instructions, then something like 4.00mm 3183TQ should do. Most manuf specify one of the HORxx type cables though so have a read of the installation instructions.
 
The butyl has stranded cable not solid core so handles the heating from the current better. The butyl is also more suitable to the environment (grease/oil etc). Wouldn't use it on an oven install but usually do for a cooker.
 
As a rule of thumb use the same size conductor as the supply circuit. So for most domestic cookers a bit of 6.0mm T&E is the norm

Every fine stranded cable requires ferrules at the terminations unless connected to a terminal specifically designed for fine stranded cables


Sent from my iPad using Tapatalk
 
What kind of cable do I need to wire a new 7.9kW cooker?

Mate you are going to get all kinds of stick for posting a question, lots of things come into play, lots of information required, length of run, installation method, type of supply etc etc, you will get more help, less grief if you ask the Moderators for access to the Trainee section, where there are like minded people there to help you, not having a dig at you but if you post a question like this one,you deserve all you get
 
Mate you are going to get all kinds of stick for posting a question, lots of things come into play, lots of information required, length of run, installation method, type of supply etc etc, you will get more help, less grief if you ask the Moderators for access to the Trainee section, where there are like minded people there to help you, not having a dig at you but if you post a question like this one,you deserve all you get

I don't mind a bit of stick, I am a trainee. Besides, the question has been answered now. Thanks for your concerns though.
 
Last edited:
with regard to your question about ferrules on fine stranded flex. this cable is not suitable for connecting in screw terminals unless ferruled.
 

Reply to New Cooker Cable in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Thanks for replying
2
Replies
23
Views
2K
allowing for diversity a 32 amp supply will be fine for them both, but remember, the cable needs to be adequate to cope with a load on up to that...
Replies
4
Views
925

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top