Okay, so I think I've made my mind up and wouldn't mind a sanity check. There's a couple lighting circuits that don't pull much so I'm going to join them in to the same breaker, creating a spare way. Then, C63 MCB as a distro circuit, running in SWA to a little 2-way DB in the room where the new circuits are going, running 2 x B32 RCBOs - they won't be anywhere near 32A at full load, but need 2 circuits as it's computer equipment and would likely trip the RCBO if all lumped together.

Should get away with 10mm SWA for CCC, but was going to install 16mm just to keep the Zsdb as low as possible. Run will be around 8m for SWA from the upstream DB, and then the 2 circuits are RFCs ran in 4mm (again, to keep that Zs down).

All sound tickety boo?
 
Should get away with 10mm SWA for CCC, but was going to install 16mm just to keep the Zsdb as low as possible. Run will be around 8m for SWA from the upstream DB, and then the 2 circuits are RFCs ran in 4mm (again, to keep that Zs down).

If there is a problem with the Zs of the existing submain then that needs to be sorted out rather than oversizing new cables to try and achieve compliance.
 
If there is a problem with the Zs of the existing submain then that needs to be sorted out rather than oversizing new cables to try and achieve compliance.

If there was a problem with the Zs of the existing submain, I wouldn't be able to get that Zs down no matter what I did. The Zs is fine - I'm just conscious I'm extending on to a long submain anyway. However, it is only a half dozen metres so I'm probably overthinking it with 16mm. I'm going to take some readings this afternoon and then I will do my cable calculations properly to ensure that circuit Zs's will be compliant.
 

Reply to New DB (additional) in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

What makes it a lack of space? I’d say to the customer to dismantle a cupboard or whatever to creat the space you need for the extra equipment...
Replies
1
Views
231
Often in old wiring, live to the downstairs switch, then in twin (or twin & earth) the two switched lives to the upstairs switch, and a single...
Replies
4
Views
351

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top