G

glasgospark

new house guys with a new heating system through mcs real scheme

3 phase supply run into house the pump is the only piece of equipment requiring 3phase ,

question is looking for best way to do this was thinking give the house itself the normal dual rcd db then from 3phase mains to lucy blocks fuse down for pump.

pump is situated in the same location as main cable head ,

4kw 32a 3phase supply required via rotary isolator


any views ?
 
If you have a three phase supply you really have to balance the phases, (I mean REALLY) So the single phase board and 3 phase switchfuse idea is out. The only way to do this is a 3 phase DB with rcbo's.
You will need to consider how to split the load, how tot make sure the accessories/equipment of circuits on different phases don't end up with touching distance of each other etc. etc.

You could maybe make your client get a single phase supply for the house and 3 phase supply just for heat pump?
 
theres already one house on estate thats done the way i described although i havent seen it yet , the pump is only 4kw , the house only has sockets lights and cooker no electric showers etc and all led lighting , i cant see there being much of a problem doing it that way
 
I'm sure something more appropriate could be sorted out for a domestic central heating pump. Sounds way over the top, to me.
 
Basic tp+n db like maybe a 4way, taking the main supply and has a breaker for the pump. (possibly then into an adjoining enclosure like a 4 module Sentry, for RCD, if required.)
Then a sp 63a mcb on L2 to feed a consumer unit also adj.
4 ways used and 8 permanent blanks.
 

Reply to new house 3phase heat pump in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
285
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
789
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
810

Similar threads

Your kWh figures are giving you consumption averaged over each hour period, but don't give an indication of total instantaneous current. To try...
Replies
9
Views
1K
Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
996

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top