I'm new to the forum to Hi!
I'm putting an installation into a Log cabin in my parents garden, I've installed the cabling installed a separate 2 way RCD protected CU in the cabin. The cable is earthed at the main CU in the house and protected on the main CU by another RCD. However I want to achieve discrimination between the 2. I see a couple of options I'd like to know if anyone is sure on the regs for this as I can't seem to find it in BS7671:2008
1) Install a time delayed RCD in the CU in the house.
2) - (This is the option I am, unsure about). - As the building is a fair distance from the main property, I'd like to earth it separately (TT system), if I do this, do I keep the cable earthed at the main CU? If I keep it earthed at the main CU does it make the entire installation a TT system since the new earth rod will essentially be connected to the main earthling terminal.
- Also if I do connect it at both ends will I still get discrimination
I hope this is clear,
thanks in advance - Pete
I'm putting an installation into a Log cabin in my parents garden, I've installed the cabling installed a separate 2 way RCD protected CU in the cabin. The cable is earthed at the main CU in the house and protected on the main CU by another RCD. However I want to achieve discrimination between the 2. I see a couple of options I'd like to know if anyone is sure on the regs for this as I can't seem to find it in BS7671:2008
1) Install a time delayed RCD in the CU in the house.
2) - (This is the option I am, unsure about). - As the building is a fair distance from the main property, I'd like to earth it separately (TT system), if I do this, do I keep the cable earthed at the main CU? If I keep it earthed at the main CU does it make the entire installation a TT system since the new earth rod will essentially be connected to the main earthling terminal.
- Also if I do connect it at both ends will I still get discrimination
I hope this is clear,
thanks in advance - Pete