New member, straight in with a question | on ElectriciansForums

Discuss New member, straight in with a question in the The Welcome Forum area at ElectriciansForums.net

Ampo

-
Joined
Jan 15, 2018
Messages
70
Reaction score
15
Location
Cardiff
Hi all, new on here. Been watching for a long time but hoping someone can help on something I've drawn a blank.
Been asked to supply temporary 4 x 63a 3 phase supplies from a genny. All the info I have is that they are pulling about 61a on each so close to the top. I need to work out kw/kva of genny but can't remember the calculation for this. If single phase I would just 61×230(around 14kw).
For 3 phase I can't remember if I just times this by 3 or do 61x400. All feeds are running motors so are balanced and on the way I will be taking off some small single phase which shouldn't unbalance thing too much. Any help appreciated
Cheers
 
GENERATOR AMP RATINGS - THREE PHASE EXTENDED
3 PHASE AMPERES - 80% POWER FACTOR*


kW Times 1000 divided by (Volts*1.73) *.80

This chart approximates the amperage of a generator based on the size of the generator and the load on the generator at 100 percent of capacity. Please note that this table is intended to be used as an estimator is not an exact representation due to various factors that can increase or decrease amperage. Elevation, temperature, fuel quality, age, wire size and length and other factors can decrease the amount of power a specific installation can generate.

Here is a link to a chart that gives you the information you require.
Generator Amp Ratings Chart, Three Phase Extended Custom - https://www.generatorjoe.net/html/genrate.html
 
Thanks for such a quick reply! Am I right in thinking then I'll need a 292kva genny total or 233kw using x 0.8?
no..... 73kVA total . (as you have stated the phase current, i've not considered PF).
 
Ok... Am I just being really thick.
The OP requires 4 feeds of 61A (3 phase)... Isn't that 244A?
According to a genny calc site that would be about 170kVA
upload_2018-1-15_11-24-48.png


If these are all running motors then the starting of the motors may affect the max amperage needed.
 
This is all simpler than I thought so I think I may be over complicating this in my head. Is it as simple as saying 61a x 230 = 14kw then x 3 for 3 phase (42kw) and then I want 4 so 168kw total (bit more for Kva) am I there or have I done this wrong
 
Been asked to supply temporary 4 x 63a 3 phase supplies from a genny

Please can you clarify this comment. What is it you actually need?
See post #6 & post #8
 
that's about right. i forgot that you'd got 4 supplies, so 42 x 4 = 168kVA. if the 61A current is a given, then forget about PF or kW-kVA. that's already allowed for if the 61A is correct.
 
Please can you clarify this comment. What is it you actually need?
See post #6 & post #8
Sorry yes the actual need is 4 separate 3 phase supplies at 63a so its 42kw for each 3 phase supply times 4. Thanks for your help guys. I had the answer originally and then completely over thought it. Back to basics
 
If the genny is powering 3 motors, that "are pulling about 61a" each, how are the motors controlled (DOL, inverter) and do they all start at the same time?
Would you not need a bigger genny for the start-up of the motors?
 

Reply to New member, straight in with a question in the The Welcome Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
957
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Gents has anyone done an application using the UKPN smart connect portal for a split phase supply and addition of multiple single phase battery...
Replies
0
Views
401
When I was on the electric board We had a pair of pillocks connect a housing estate to a very large genset, the n lead was in two parts and not...
2
Replies
28
Views
4K

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top