Assuming the Ze was measured with the main protective bonds disconnected that is far too high and with those Zs readings it sounds like it is being earthed by other means.
 
or the Ze is 0.21 after the tester went to specsavers. i.ve frequently come across TN-S at well under o.8. at home it's 0.18.
 
Something in the information does seem a little strange. If the supply EFLI is that much though then as stated on the Condition Report guidance for recipients:

Where inadequacies in distributor's equipment are encountered, it is recommended that the person ordering the report informs the appropriate authority.

But naturally, it is up to the skilled person to identify the inadequacy and provide accurate information for the person ordering the report to actually report it.

But I very much doubt those readings are accurate.
 
only just got in after an investigation into paul's post regarding his security lights.
 
first fault is a cross connection between the upstairs socker rfc and the disused immersion heater radial, so the upstairs sockets get fed from 2 separate MCBs. this I will need to trace out after moving loads of itchy-poo.

2nd fault is the diabolical installation of the security lights. cpc's sleeved and used as switched L's on 3 cables. metal floodlights not earthed. no RCD protection on installation. I have disconnected for obvious reasons. Paul has requested a quote to rewire the security lights with new LED floods and PIRs, and to sort out the X-connection.
 
The next loft space I go up into, that's got more stuff than Big Yellow Self Storage, I'm going to take a picture and start a new thread.
 
as in.......

upload_2017-7-13_15-41-18.jpeg
 

Reply to New Member with an EICR question on max Ze reading in the The Welcome Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
271
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
770
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
776

Similar threads

FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
2
Replies
21
Views
2K
If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top