New metal 2 way unit fed from old Plastic 10 way consumer - Ok or not ? | on ElectriciansForums

Discuss New metal 2 way unit fed from old Plastic 10 way consumer - Ok or not ? in the UK Electrical Forum area at ElectriciansForums.net

alPudsey

DIY
Joined
Oct 27, 2021
Messages
6
Reaction score
3
Location
Leeds
Hi,

I have just had work done but not sure if this is acceptable as i am having doubts.

I have an existing 10 way 'Plastic' consumer unit, fitted in 2004.
Electrician has now added a new 2 way METAL unit to feed the dormer Ring mains and Lights & the tails are fed to inside the old 10 way (not from a splitting Henley block).

Even if it is correct, would they have to test the old consumer unit and circuits as well ? , as new one is being from the internals of the old one ? Some of the existing circuits did trip a few times when he was working on it, hence why Im asking about 'testing' of old one

Can you feed a new consumer unit directly from the inside of exsiting old one ? If yes, would installation testing have to include the old consumer too or not ?
 
How do you mean 'from the internals'?
If he has fed the new CU from an existing or spare way, the supply circuit only should be tested not the other circuits on the existing CU.
If 'from the internals' you mean he has connected into the top of the main switch/isolator, not ideal but the main cutout might be providing the OCD for the supply circuit? Again, existing circuits need not be tested.
 
It depends on what "tripped" when he was installing. All he really needs to check is the EFLI for the circuit and that the MCB for the circuit to the new mini board is correct for the cable. No need to do anything with the exsiting circuits, if no work has been done on them.
 
The feed to the metal board should be provided with circuit protection via an MCB in the plastic board for a 5sec disconnection time.....NOT from the top of the incomer in the plastic board...
Can't see any problem feeding from the top of the main switch IF the main switch has sufficient capacity for the extra tails, the connection can be made without excessive copper showing and at the same time be secure, and the new tails are sized sufficient for the design load of the new board.
And the total length of the tails from the meter still doesn't exceed 3m.
 
Last edited:
Can't see any problem feeding from the top of the main switch IF the main switch has sufficient capacity for the extra tails, the connection can be made without excessive copper showing and at the same time be secure, and the new tails are sized sufficient for the design load of the new board.
If the meter tails to the plastic DB were 3m long and then you fed another board from the supply terminals of the main switch in the plastic board, could this been seen as having the meter tails being longer than the 3m recommendation from the DNO?
 
My preference when adding additional fusebox/CU is to take from source splitting tails/ Henley block etc, jumping off main DP incomer forget that not for me. As for using a spare way to create sub circuit to a new CU not for me neither.
 
My preference when adding additional fusebox/CU is to take from source splitting tails/ Henley block etc, jumping off main DP incomer forget that not for me. As for using a spare way to create sub circuit to a new CU not for me neither.
Do you provide an isolator for each new board you add in? Or if there's already one fitted after the meter do you use this to feed the Henley blocks first which in turn feed both boards?
 
Do you provide an isolator for each new board you add in? Or if there's already one fitted after the meter do you use this to feed the Henley blocks first which in turn feed both boards?
I didnt mention isolators but yes would utilize existing (if one there or fit) on outgoing then fit my henleys so yeah only one to control the additina boards.
 
Can't see any problem feeding from the top of the main switch IF the main switch has sufficient capacity for the extra tails, the connection can be made without excessive copper showing and at the same time be secure, and the new tails are sized sufficient for the design load of the new board.
And the total length of the tails from the meter still doesn't exceed 3m.
You should be using phase blocks to split feeders in my book...

I've seen it before and I don't like it
 
If the meter tails to the plastic DB were 3m long and then you fed another board from the supply terminals of the main switch in the plastic board, could this been seen as having the meter tails being longer than the 3m recommendation from the DNO?
This 3 meter rule/ reg is often mentioned. There is no reg that states this.
in some cases 10 meters is perfectly acceptable in others it’s not.
 

Reply to New metal 2 way unit fed from old Plastic 10 way consumer - Ok or not ? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
956
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Personally, I would take a Ze measurement myself rather than rely on someone else's maybe drive by scrap of paper.
2 3
Replies
31
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top