Continuity tests shouldn't show negative results, you can't have negative continuity!
Displaying the less than symbol, a negative value or just an error message would all achieve the same thing, it alerts you to the fact that the nulling of the leads is wrong.
Whether the null is off by 10ohm or 0.1ohm doesn't really matter as it is wrong whatever and needs to be addressed.
My antiquated Fluke 1651B has none of these below 0 warnings , but I created a 0.07 Ohm confirm "0" ...nulling leads repeatedly over a short duration can result in differences that usually range no more than 0.08 ohms.
@Sparks82when carrying out 3lead low trip zs.
Do you use the kewtech leads with the megger Steve? Any particular ones? Link please ?I have one, I love it. Good bits (not saying other manufacturers don't do these things...) :
- 2 lead RCD test. No need to faff around with a neutral connection (common on all Meggers)
- Use the same 2 leads (red and green) for Ze, PEFC, and PSCC (on single phase), on the same setting: I don't bother using the separate "L-L" setting on the dial and plugging in the blue lead to measure PSCC on single phase, I just use the "L-E" setting (on "2Hi") and put the green lead on N
- Quicker, and possibly and more accurate low current Zs than other Meggers, I like the confidence indicator
- 100V IR for when you're fairly confident, but not totally confident, that there's nothing plugged in. Useless for test results, but fantastic for verifying that nothing's plugged in
- I like the long thin pointy probes, for getting in some tight spots
- Bag is great for carrying all my testing bits (jump leads, R2 adapter, lightmates etc), over-shoulder strap means I can carry my toolbox in one hand and my little ladders in the other
- in "3Lo" Zs mode, you can tell it there are Type B RCDs in play (long press on <-> ). Even if there aren't, and it's just a tetchy Type AC RCD (or maybe a lot of inherent leakage current), it's sometimes useful for getting a Zs result without using The Alternative Method (or, when you really, really don't want to trip an RCD!)
Negatives (common to all Meggers, I think):
- It's far too easy to "un-null" your leads when on continuity setting. Pressing either of the test buttons - which is very easy to do, there's one on each side and just knocking one will do it - will remove the saved null setting. A right pain in the **** if you're the other end of a wander lead! So quite often I either turn it off, or just put it on a different setting, if I'm carrying it around on my neck
- Would be nicer if the backlight light stayed on a bit longer
- Usual Megger lead incompatibility with most third party bits and bobs, so I have a couple of cheap Kewtech leads to connecting to wander lead, lightmates, R2 socket etc.
A basic set of 2 leads is all you really need, this one will do: Kewtech ACC020S Test Leads - https://www.screwfix.com/p/kewtech-acc020s-test-leads/28760Do you use the kewtech leads with the megger Steve? Any particular ones? Link please ?
Reply to New MFT - opinions in the Electrical Tools and Products area at ElectriciansForums.net
Thanks for visiting ElectriciansForums.net, we hope you find the Electricians Tools you're looking for. It's free to sign up to and post a question yourself to find a tool or tool supplier either local to you, or online. Our community of electricians and electrical engineers will do their best to find the best tool supplier for you.