hi just bought a new oven
its a 4.4KW
i`m running a 6mm cable from the cu using a 32mcb to kitchen around a 6M run under floor boards then 2m in trucking to a 45amp cooker socket
just wondering the security mcb is dismantled
best to place the 32mcb in here or put the 32mcb left of the dinning room mcb
thank you paul
[ElectriciansForums.net] new oven advice needed please
 
That split load Consumer unit hasn't been wired the best in all honesty. It would have been better mixing the lighting and sockets across the 2 RCD's. You could correct this but it makes for more work and can get a little confusing depending on your knowledge level (i have seen someone do similar and not take over the corresponding neutrals for the circuits.

Anyway, it doesn't matter which side the new cooker circuit goes on to, imo it would be better on the RHS which it looks like there is room for at the side of the security mcb if you remove the blank?
Have a look at part P also as i believe this to be notifiable work.
 
New circuit, Needs notifying to building control, Will need an EIC and if putting on RCD side of board RCD will prob need upgrading. I would put it on the right hand side to balance the board a bit better and use a Type A RCBO ....Get a sparks in
 
That split load Consumer unit hasn't been wired the best in all honesty. It would have been better mixing the lighting and sockets across the 2 RCD's. You could correct this but it makes for more work and can get a little confusing depending on your knowledge level (i have seen someone do similar and not take over the corresponding neutrals for the circuits.

Anyway, it doesn't matter which side the new cooker circuit goes on to, imo it would be better on the RHS which it looks like there is room for at the side of the security mcb if you remove the blank?
Have a look at part P also as i believe this to be notifiable work.
It does, only one side is rcd protected. It has to go on the rcd protected side.
 
Yeah my bad there........ive been looking at that many CU's from photo's these last few days that i saw 2 rcd's! Thats what you get for being up at 5am with baby in hand! Best ignore my first post which would have been sound advice if there were 2 rcd's.......which there aren't.

It is ofcourse a main switch and 1 RCD, i would refer to it as a 16th CU normally. If CCU has socket outlet it needs to go on the LHS.
 

Reply to new oven advice needed please in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
361
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
921
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Obviously not a building/DIY forum so will keep it short but yes - we've taken all the floors up. Several joists in the bathroom need doing as...
Replies
8
Views
2K
K
  • Article
Advice needed - questions before getting new bathroom fitted Hi all, hope this is okay to post. Just over a year ago, I took on my dad's old...
Replies
0
Views
215
KamikazeBob
K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top