T

taslaw

I have just bought a neff 2.9kw single oven; it replaces an oven that was hard wired on to a dedicated oven circuit on a 32a mcb with 6mm cable. My electrician says that he will just wire the new oven onto the same system. I am no expert, but thought that the mcb is too big for this oven , would it not be prudent to reduce the size of the mcb? thanks.
 
that 32A MCB is sized to protect the 6mm cable. nothing to do with the rating of the oven. nothing to stop you downrating it though. if you are concerned, then you could put it on a 13A FCU.

- - - Updated - - -

beaten by the monkey.
 
I would be reluctant to use a switch fuse on a 3 Kw load (you can but often see them burnt out ) its a dedicated circuit feeding a fixed load, use a 16 A mcb type b job done.
 
I have just bought a neff 2.9kw single oven; it replaces an oven that was hard wired on to a dedicated oven circuit on a 32a mcb with 6mm cable. My electrician says that he will just wire the new oven onto the same system. I am no expert, but thought that the mcb is too big for this oven , would it not be prudent to reduce the size of the mcb? thanks.

What do manufacturers instructions say regarding OCPD? These will have to be followed.
 
What do manufacturers instructions say regarding OCPD? These will have to be followed.

Not some of the manufactures instructions i've read you wouldn't!! lol!! Many of these instructions are based on European standards and wiring methods, rather than on your BS7671. Some, like the recently posted ''humidistat'' are just an outright joke!! lol!!
 

Reply to new oven in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
257
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
739
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
721

Similar threads

  • Question
Thanks so much for all the responses guys! It seems that what I'm planning is nothing unusual or regs-busting. I'll hook it all up and have a...
Replies
7
Views
3K
  • Question
Why not fit a self contained SPD fed directly from the Henley blocks, and free up a bay? Could probably make one up from whats there, using a...
2 3 4
Replies
47
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top