New shed circuit tripping RCD at house consumer unit | Page 3 | on ElectriciansForums
Discuss New shed circuit tripping RCD at house consumer unit in the UK Electrical Forum area at ElectriciansForums.net
solgen
Hi,
I've recently run 4mm 4 core SWA from a 20A MCB house consumer unit to a garage unit installed in a shed 50M away. The garage unit has 16A and 6A breakers protected by 40A 30mA RCD main switch. All wiring connections seem to be correct, however, as soon as anything is placed under load either from socket or light, the RCD back at the house consumer unit trips. I have visually inspected everthing so far and cannot see any problems.
I looked for neutral problems and cannot see anything amiss.
Can anyone suggest where the problem maybe?
Its unusual for a supply cable to affect an RCD but it does happen...
Garden electrics are such a pain ........... and hence why its best not to have them connected to a RCD which also protects house circuits..
if it's the RCD in the summer house that's tripping, then it's 99.9% that the fault is downstream of that RCD. the feed to the summer house is not going to be the problem.
I think the op just needs to get his tester out and give us some readings
trip times on both rcds?
Don't need 2 RCDs not unless the shed feed is from a non RCD side of the CU, in this case it looks very doubtful that it is, as the house RCD is tripping
Reply to New shed circuit tripping RCD at house consumer unit in the UK Electrical Forum area at ElectriciansForums.net
Given that, it probably makes sense to TT the shed, unless you can be sure it doesn't act as an extraneous-conductive-part. (The SWA won't have...