Good morning,

I've been thinking of the best way to supply my garage with a new fuse board from the cut out.

I've PME an new 80A cut out.

My thought is: split incoming with henley's, install a 50A or 63A dp switch near the cutout.

Use 2 core swa 10mm or 16mm to supply the new db. With a sperate earth stake in the garage and not connect swa in the garage db.
I'll use 10mm or 16mm earth to connect earth stake.

The run is 14M and I've a trench dug out. I don't want it in the main db. The main db is fully populated with rcbo.
I have 1 spare way but do not want to use it.

The garage db supplies the garage, shed and the conservatory at present.

The previous owner was a handy man.
I'll keep the circuits as is.

The garage board is a hagar with no rcd at present. Thought to change out the main switch or just full populate with rcbo.

Any concerns please?

Regards Millo
 
If you do as you propose, how will the SWA be protected from overload/fault current?
 
The garage db will be supplied from the double pole 50A or 63A circuit breaker from the henley blocks. The main house db will be supplied direct from the henley's.

Safe isolation for garage db.
I could use a rcd with time delay and or 100mA for discrimination on the 30mA in the garage. But this might be a bit over kill. ?

Thank you for you help
Regards

Millo
 
Kingeri, your quite right I didn't.

The dp 50 or 63A will be the circuit breaker not just a dp switch.

This will be isolation and protection.what would you recommend? 63A MCB? Assuming the cables current capacity is higher.
 
Kingeri, your quite right I didn't.

The dp 50 or 63A will be the circuit breaker not just a dp switch.

This will be isolation and protection.what would you recommend? 63A MCB? Assuming the cables current capacity is higher.

This should be worked out with your cable calculations. Are you an electrician ? I'm asking because this is posted in DIY.
 
Kingeri, your quite right I didn't.

The dp 50 or 63A will be the circuit breaker not just a dp switch.

This will be isolation and protection.what would you recommend? 63A MCB? Assuming the cables current capacity is higher.

Can we clarify you understand that a DP isolation switch does not give you overload protection here, your responses are somewhat ambiguous and do not give clarity on this point and the mcb comment seems to come as an afterthought following a response to your post. As you have not filled in your profile I need to try gauge your understanding through direct questioning of what may seem very condescending questions if you are fully qualified.
Is there any reason why you are isolating the garage from the main earthing arrangement, this would be a last resort given you have an excellent reliable PME system to utilise the earth from, are there any reasons you wish to install a less reliable method like an earth rod?
 
I qualified a while back, but wasn't clear in my write up.

I am looking to protect the SWA and to discriminate between the 2 db's.

There is no reason that I cannot use PME.
I didn't want to cause a posSible issue with the main db.

The cutout has only just been changed to PME a few days back, the system was TNCS.

I will fill in the profile section soon enough as I only joined today.

So 50A or 63A MCB depending on cable size.

Use the PME

Use rcbo on circuits in garage db
 
Discrimination is normally referring to short circuit fault currents tripping devices not overload ratings and in domestic you will rarely achieve discrimination unless you have a 200amp supply so your responses are somewhat confusing, can you elaborate better on your design and why.
 
It was a TNS system. Seperate earth from the neutral.
Now its been linked in the new cutout.
TNCS or PME you are quite right.


All I would like to do is split the supply through henley blocks.

Direct connect the main db to the henley's.

Install a protective device in the meter cabinet for the new supply cable.


I do not have the cable, as I pointed out it will be either 10mm or 16mm SWA. Hence the 50A or 63A protective device (MCB)

Cable design has determined the max current. Hence 50A for 10mm and 63A for 16mm will be ok.

I'll install a 30mA RCD in the 2nd db or use RCBO.
 
How can you split it at the cut-out? Surely you have a meter fitted, so you either split it after the meter or two meters.
 

Reply to New supply for garage, split from cut out in the DIY Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
961
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Sounds more positive.
Replies
8
Views
630
This is the point of having a trainee badge... it allows you to ask simple questions without the critism reserved for have-a-go heroes. Things...
Replies
5
Views
349

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top