To comply with the volt drop requirements at 150m then you would need to be limited to 25A to use 25mm² SWA.
This would allow for no VD at all on any of the final circuits RB
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss New supply from transformer mast for 9 separate metres property connections? in the Commercial Electrical Advice area at ElectriciansForums.net
To comply with the volt drop requirements at 150m then you would need to be limited to 25A to use 25mm² SWA.
Wrong forum, but have you got the costs for New Water supplies?
And Foul drainage connections or is it Biodigestor?
All of which is WHY i asked about the distances involved questions above!! ...lol!!
The other question that should be asked, is how are you (OP) intending to run these supply cables to each plot?? Without knowing the layout, the distances may well need to be in excess of what your planning. Eg, are these cable routes following paths/road or as the crow fly's, crossing the other plots underground?? If the latter, you may need to go deeper than the recommended 600mm (60cm) and be run in heavy duty ducting....
View attachment 24708
Here is the cable calculation for 10mm cable at 150m - he intimated it would give 25 amps at 5% VD.
The above doesn't make much sense to me.
I don't know much about his design software, but if that's what he's saying then he's wrong I'm afraid, very wrong!
On a 10mm three core thermosetting SWA, 25A over 150m results in a voltage drop of 17.6V, or 7.6%, 2.6% over the maximum allowed for general circuits according to the guidance given in appendix 4 of BS 7671.
Is this a wind up? It was Friday yesterday.
For someone to buy a plot of land with such obvious problems beggars belief.
As for this being a self-build, it has all the hallmarks of a disaster epic. Lots of money sinking without trace.
Given the problems with the electricity, water and sewage I would suggest you employ a project manager that knows what he is doing.
Your comment “I’m not running cables for others” is incredibly short sighted. As for your plot having its own potable water and sewage arrangement is bordering on stupidity.
You would seem to have alienated yourself from the other owners and now you’re going to pay for it.
But as it’s your money, do as you will.
I assume you are paying this supposed “engineer” for his services, I find it somewhat offensive that you come here expecting total strangers to assist for nothing.
I'm not laying any cable for anyone else... just our own plot.
There is a 10mm cable laid in at the moment, which isn't of any use to us - maybe a temporary supply for plugging in tools - that would be useful and save on petrol with the generator! Max load would be 25 amps as suggested by the engineer and calculations above.
Not crossing any plots, following the road. It has been measured countless times. 115m to the edge of the plot, then another 30m to the entry point in the dwelling.
I didn't think for a moment that you were, i was referring more, as to how these cables would be routed from the central position to the individual plots... Which you have now cleared up, by you stating that you are following the road.... Are you running this buried cable in ducting, or just direct buried??
Don't be tempted to run 2 core SWA rather than 3 core, using the Armour as the earth, it won't comply with main bonding requirements. To cut costs and reduce cable size, consider using 2 smaller cables in parallel. Direct cable burial over a 150m is going to need a lot of man hours to remove sharp stones and other debris from the cable trench floor and sifting of excavated soil for the first backfill layer after the soft sand. It could well turn out cheaper to duct the cable, which if planned correctly, could provide a means of replacing the cable(s) in the future, should it be deemed necessary....
Oh and if i were you, i'd get everything in writing from this Electrical Engineer you talk about. Is he the guy that produced the cable size print out you posted, because there are a few fundamental data errors on that calculation sheet??