As far as im aware the spilt is ok to run underground via a duct something to do with the neutral and earth wrapping aroung the live conductor ,and as far as the rcd on the mains side of the submains i can drop it i was just looking little advise so cheers lads
 
But still underground and needing an earthed armour or similar

If the duct provides equivalent protection against mechanical damage as armour or metal sheath, then it's not required. BYB 522.8.10. I'd say that typical soil pipe probably does, although in most cases I'd use SWA anyway.

Interestingly, it doesn't seem to matter that the duct doesn't provide the earthing to a conductive tool that an earthed armour would.
 
As far as im aware the spilt is ok to run underground via a duct something to do with the neutral and earth wrapping aroung the live conductor ,and as far as the rcd on the mains side of the submains i can drop it i was just looking little advise so cheers lads

Any thoughts on this question?:
What's providing the overcurrent protection to the 30m underground cable?
 
If the duct provides equivalent protection against mechanical damage as armour or metal sheath, then it's not required. BYB 522.8.10. I'd say that typical soil pipe probably does, although in most cases I'd use SWA anyway.

I wouldn't claim that the protection is the same as earthed armour, however, unless you had a considerably dense steel duct to actually prevent penetration. It is the fact that the armour is earthed which is pertinent.

As for split concentric there is a live conductor surrounding the phase conductor in places, so this couldnt really be considered to be "protecting" it.
 

Reply to New supply to new build in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Your kWh figures are giving you consumption averaged over each hour period, but don't give an indication of total instantaneous current. To try...
Replies
9
Views
899
  • Question
even allowing for diversity this sounds a bit tight for a 100 amp supply, can you tell us what the existing circuits actually have connected to...
Replies
2
Views
626
If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K
  • Question
In terms of meeting end-end voltage drop I doubt it will help you save much copper unless the areas to be served are physically close to that...
Replies
1
Views
956
  • Question
investigated a little bit more today and noticed a piece of metal connected externally to the incoming head which was bolted to some copper earth...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks