As far as im aware the spilt is ok to run underground via a duct something to do with the neutral and earth wrapping aroung the live conductor ,and as far as the rcd on the mains side of the submains i can drop it i was just looking little advise so cheers lads
 
But still underground and needing an earthed armour or similar

If the duct provides equivalent protection against mechanical damage as armour or metal sheath, then it's not required. BYB 522.8.10. I'd say that typical soil pipe probably does, although in most cases I'd use SWA anyway.

Interestingly, it doesn't seem to matter that the duct doesn't provide the earthing to a conductive tool that an earthed armour would.
 
As far as im aware the spilt is ok to run underground via a duct something to do with the neutral and earth wrapping aroung the live conductor ,and as far as the rcd on the mains side of the submains i can drop it i was just looking little advise so cheers lads

Any thoughts on this question?:
What's providing the overcurrent protection to the 30m underground cable?
 
If the duct provides equivalent protection against mechanical damage as armour or metal sheath, then it's not required. BYB 522.8.10. I'd say that typical soil pipe probably does, although in most cases I'd use SWA anyway.

I wouldn't claim that the protection is the same as earthed armour, however, unless you had a considerably dense steel duct to actually prevent penetration. It is the fact that the armour is earthed which is pertinent.

As for split concentric there is a live conductor surrounding the phase conductor in places, so this couldnt really be considered to be "protecting" it.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
New supply to new build
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
34

Advert

Thread statistics

Created
steviethespark,
Last reply from
Simonslimline,
Replies
34
Views
3,598

Advert

TrueNAS JBOD Storage Server

Back
Top