I'm replacing an old MEM Fuse Board in my garage with a Small CU. The power was supplied from the ground floor ring main, so I've removed that and added a separate circuit in the main CU with its own RCBO. Problem is, the RCBO trips every time I turn something on and I can't understand why. Apart from the supply cable - main CU to new CU - the cabling is exactly the same as yesterday and was working so I can't understand why there's a problem. Help desperately needed as I have 3 freezers in the garage.
 
Have you done any testing? Check there is no short to earth. You say every thing is the same but how can it he if you have taken away the power from the ring and put a new cable in to feed it.

Sounds like maby the cable is damaged and needs to be tested.

If you used twin and earth then it is very easy to damage the cable and cause a short.
 
I'm replacing an old MEM Fuse Board in my garage with a Small CU. The power was supplied from the ground floor ring main, so I've removed that and added a separate circuit in the main CU with its own RCBO. Problem is, the RCBO trips every time I turn something on and I can't understand why. Apart from the supply cable - main CU to new CU - the cabling is exactly the same as yesterday and was working so I can't understand why there's a problem. Help desperately needed as I have 3 freezers in the garage.
my area of operation. sen d me a pm and i'll come and sort it.
 
A pic of the wiring inside the new CU might help (or might not). Also a pic of the wiring to the RCBO.

Pretty hard to diagnose remotely without a full set of tests.
 
If I had my way you would be in court, changing a distribution board and having no idea how to sort out a minor issue should be a criminal offence IMHO. Lets step back actually, are you an Electrician? have you got any test kit? Popcorn ready.
 
If I had my way you would be in court, changing a distribution board and having no idea how to sort out a minor issue should be a criminal offence IMHO. Lets step back actually, are you an Electrician? have you got any test kit? Popcorn ready.
I trained as an Electrician with the RAF in 1975 and I've been doing it since. As I'm now retired I don't have a full range of professional test equipment, just my trusty Multi-meter. I'm sure this is something trivial, but I'm struggling to find the answer and thought I would try and get some help in case I'm missing something bleeding obvious. Most of the comments have been helpful.
 
Well firstly thanks for your service, I have high regard for service personel. Now that aside you should know better as an ex spark, changing a board and connecting existing circuits to it without testing is literally appalling, sorry but there you are, you will get the odd nice comment but it will be few and far between I am afraid.
 
Hi - I would get hold of some extension leads sharpish and get the freezers back on power. It will be tough to find the fault(s) without test gear.
 
Hi - I would get hold of some extension leads sharpish and get the freezers back on power. It will be tough to find the fault(s) without test gear.
Too true, there may be beer in the fridge.
 

Reply to Newbie screaming for help with constantly tripping RCBO. in the DIY Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
439
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

The power company only brings in 3 wires which is 2 live and 1 neutral wire. It’s our responsibility to add the ground rod to bond the neutral...
Replies
3
Views
618
  • Question
Fantastic thanks Freddo that last photo confirms all your suggestions so I’ll get back over and remove the links and test. Thanks again!
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top