There is an unfinished sticky on DIY electrics on this forum. Me thinks we need a full and clear sticky explaining that replacing a CU is not as simple as most think.
1. Replacing a CU comes under part P and it is illegal to.... a.Do so without notifying BC.....and b. without complying with Bs 7671.
2.Notifying BC yourself will probably cost more than paying a registered electrician to carry out the whole thing.
3.Complying with 7671 will include tests/inspections to verify the effectiveness of earthing and bonding,and tests and inspections to verify existing circuits are in a fit state to be connected to a modern CU.
4.A modern RCD protected CU will pick up faults and incorrect connections that your old CU wont.This is why tests are carried out before and during the replacement. These tests can only be carried out with proper equipment and the knowlege to use it. A neon screwdriver....martidale plug in tester....or multimeter will not carry out the required tests.
5.Those who think it's a simple swap will inevitably end up in the same boat as the OP here,and even if it works they may still have a dangerous CU without knowing it......and will have broken the law.