No Discrimination | on ElectriciansForums

Discuss No Discrimination in the UK Electrical Forum area at ElectriciansForums.net

Joined
Jul 9, 2011
Messages
151
Reaction score
12
Location
Cardiff, but work SW
Evening guys,
Query with discrimination. Main DB with 30m/A RCD feeding another sub board with 30m\A RCD. The RCD in the main DB is tripping out before the sub board RCD. Am I able to change the Main DB RCD to a type S? (All that Main RCD is feeding is two sub boards, twin and earth fed in an office. Thanks in advance..
 
Then unless the cable is in earthed metallic protection or more than 50mm from the surface if in a wooden stud or in a metal stud then it requires additional protection by a 30mA RCD. You can’t get a type S 30mA RCD.
 
#5 You wouldn’t need the main RCD or you wouldn’t need the sub RCD?
It’s a two year old installation by the way. Was thinking about changing the main 30m/A RCD to a 100m/A type S but obv can’t because it need additional protection. Hmmmmm
 
If it's only a couple of years old sounds like poor design for a submain to require additional rcd protection. If it had been pre additional protection for cables in walls you may have had an argument although tenuous for removing it but as it stands it would be a bad idea.
 
You need to know what is causing the tripping fault or combined excess natural leakage. Is it both supplies or just one. Do you have an earth leakage clamp meter.
 

Reply to No Discrimination in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
2
Replies
17
Views
808
  • Question
Many thanks all. Very helpful to be able to bounce these things around. Was fairly happy with it all initially, but once the seed of doubt is...
Replies
8
Views
842

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top