No Earth available at the cut out? | on ElectriciansForums

Discuss No Earth available at the cut out? in the UK Electrical Forum area at ElectriciansForums.net

C

craig1000

Hi need to clarify as quickly as possible a situation?
No clear main earth terminal at the incoming suppy?
small bit of stranded remains off the cable sheath but nut soething to connect to.
Definatly no earth rod!
I want to split the incoming supply after the meter via 100amp link blocks to provide a sub board to use for new circuits to be rcd protected feeding the kitchen & bathroom.
Customer doesnt want a full board change for fear of old wiring not holding in on a rcd.
No where to connect by earth from my new CU.
Can get a good Ze of 0.11 off the existing wylex rewirable CU but i am positive this is reading through the gas & water bonds & possibly even the cpc's in the outgoing circuits somehow.
Customer doesnt want me investigating & the cost involved of additional works the old wiring.
The DNO are not interested but should push them harder to come out & provide a MET?
Should they charge for this?
Should i put a rod in, trouble being in a built up street so where would be a problem.
Supply is a T-N-S fed via old lead paper underground cable.

Advice needed ASAP?

Thanks in advance!
 
if there's the remains of a TN-S earth, then DNO are obliged to repair/maintain this at no cost. get onto their emergency number. tell them it's dangerous, and that you have isolated the supply and the customer has got no electric.
 
Also explain to customer you will be required to fit a 100amp switch fuse to give 1 point of isolation for the whole installaion, after costing this up including Henleys, seperate board and fitting you will looking at a similar price to just replacing the board on its own..... Explain to customer your report will highlight any isues with existing wiring but unless its potentially dangerous you will connect back up as is and leave it at that if that is what they wish, Gas and Water bonding should be including and already assessed with the work you have been ask to do.
Makes me laugh sometimes how people will spend thousands on new kitchens bathrooms etc while the house electrics are falling apart then cry poor boy when its highlighted.... arse about --- comes to mind.
 
Last edited by a moderator:
As Telectrix stated, if there are definite signs of a previously DNO earthing provision from there PILS cable then they are obliged to maintain that provision.

Have you taken a Ze reading using the lead sheath as your earth?? I would confirm first, that the lead sheath is still providing a good earth provision, then you can know, if they are going to PME the supply or not... Either way, the obligation to maintain there existing earthing provision remains the same!!
 
Last edited by a moderator:
........ IF you can get someone on the phone........ IF they know what you're talking about...... IF you don't get cut off mid conversation....... IF you don't get transferred to an answer phone.......IF they'll come out within a fortnight.....
 
Hey everyone, thanks for your replies!
Did the job, & could not get the DNO to come out definite signs of an earth there previously & got a good reading from it. When telling them this & saying i thought it was there responsibility to maintain it all they would respond with is we don't install that type of system, all we do now is PME & its the customers responsibility to get an earth.
Didn't get a cost from them as he said it would need to be refereed to their regional field office for a quotation. told me to install a rod, & if i still wasn't happy to arrange a quotation.
My first dealings with DNO & aren't the infuriating in their attitude?
Got a good enough reading from the rod so all ok but its bloody mad their attitude.
Darkwood-Yes its madness the attitude of some customers, , you cannot put a price on life yet clearly some people are prepared too. Fancy fitting & furnishings yet no to electrical safety!
 
I agree with Guitarist. Repairing this broken TNS earth is absolutely the DNO's responsibility. I think DNOs are normally pretty good at this sort of emergency stuff, but the problem is often getting them to understand what the problem is. if you can convince them it's dangerous and requires an emergency response they are usually there within a few hours.
 
First spoke to them yesterday evening & at that point they were sending someone out within 3-4 hours to assess it & repair if needed! Myself willing to wait there, & then we return to the customer who clearly in my experience has no regard for electrical safety! Asked us to ring the DNO back to cancel them coming out as with all the work that had been going on he wanted to get out the house & away from it all. As much as we insisted it needed looking at unfortunately had to do as the customer wanted & cancel as if we didn't he or we wouldn't of been there when they came out. Rang back this morning, different staff member & different attitude. As i say this is my first experience dealing with them DNO i tried to be insistent but clearly not enough, not knowing the full responsibility's myself of who's job to provide or maintain. A grumpy customer & the easiest was to install a rod which is safe enough but it could be far better. Have advised the customer to further pursue the matter but very much doubt they will. ;-(
Maybe some slight in experience from my behalf but certainly something i shall be more aware of in the future! I come from a mainly commercial contracting back ground & have only recently gone into domestic & my own work!
 
Craig, you’ve done exactly what they wanted, you’ve now taken the responsibility from them on to yourself.

Don’t give up at the first hurdle, keep dogging them. It’s the DNO’s problem not yours.
 
Tony- Yes it would appear I have & I wont make the same mistake again! As I said I come from a commercial back ground & have only just gone into domestic for myself so there's plenty I am unsure about.
Richy3333 & Dingledong-Thanks for that advice I shall go about doing that then. Any suggestions on the wording exactly? & on what? as a note on the cert?
What i have installed is safe & within limits during testing it could just be better, i.e loop readings are not amazing or as low as they would be a better earth path if through the lead of the cable or if changed to PME rather than the earth rod!
Where does my responsibility lie as i have not changed or touched his existing circuits on the existing consumer unit? The work i have installed all complies with current regs.

I wanted to do a full board change but he would not allow it even with my recommendation, to worried about old circuits holding in on a RCD.
Judging by what we ripped out the kitchen he has had work done by a DIYer at some point or had a go himself.
I hope not to make people think i dont know what im doing etc but coming from a commercial back ground into domestic is different & i would rather ask questions to get it right than bury my head in the sand & get it wrong, being honest. I have done my 17th & do have all literature & do look into it but sometimes the wording can confuse or it can be quicker to ask ;-)
Not trying to get my job done for me with your knowledge but with help! Sorry had to put as do feel slightly embarrassed not knowing ;-(

On another note,if i work on a lighting or any circuit in someone's house, which is not up to 17th do i force the issue that i must upgrade it to 17th & get it on a RCD or can i work on it & leave it just MCB protected as long as the test results comply?
 

Reply to No Earth available at the cut out? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
271
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
766
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
774

Similar threads

  • Question
I'm assuming the cable will have to be cleated well to hold it in place anyway, as a stuffing gland ain't going to hold it tight like a SWA gland...
Replies
10
Views
703
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
945

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top