Hi guys
Just thought Id share with you what happened today.
In middle of re-wire, came to the board change, had checked on first inspection and discovered that instead of BS1361 there was a metal clad contraption painted red, so told the owners to contact scot power manweb asap and get it changed.
scot power manweb told them unless they pay 300 quid they are going to bottom of list and could take 3 months
I undertake re-wire, inspect this thing totally today and discover there is NO supply earth whatsoever.
you open this metal clad contraption, there are 2 porcelain re-wirable cartridge fuses one in line and one in neutral, out of these come manky wax thread covered aluminium tails
rang NIC to find out where i stood as new board going in tomorrow, where am I to earth to and where do I stand on testing etc??
told me check inside see if earth facility if not I have to install earth rod in garden
checked and NO earth facility, just a bitumin covered mess and no main eartth inside wylex re-wirable board.
so for however long this house has had NO EARTH to speak of and manweb want to charge 300 quid to put it right!!!
needless to say as of tomorrow there will be an earth rod and new board and the home owner has stayed elsewhere over night as I refused to re-energise the house in its present condition
I was speachless
Just thought Id share with you what happened today.
In middle of re-wire, came to the board change, had checked on first inspection and discovered that instead of BS1361 there was a metal clad contraption painted red, so told the owners to contact scot power manweb asap and get it changed.
scot power manweb told them unless they pay 300 quid they are going to bottom of list and could take 3 months
I undertake re-wire, inspect this thing totally today and discover there is NO supply earth whatsoever.
you open this metal clad contraption, there are 2 porcelain re-wirable cartridge fuses one in line and one in neutral, out of these come manky wax thread covered aluminium tails
rang NIC to find out where i stood as new board going in tomorrow, where am I to earth to and where do I stand on testing etc??
told me check inside see if earth facility if not I have to install earth rod in garden
checked and NO earth facility, just a bitumin covered mess and no main eartth inside wylex re-wirable board.
so for however long this house has had NO EARTH to speak of and manweb want to charge 300 quid to put it right!!!
needless to say as of tomorrow there will be an earth rod and new board and the home owner has stayed elsewhere over night as I refused to re-energise the house in its present condition
I was speachless