Evening all,

I have arranged to go and see a job on Wednesday with the following problem: The customer has a disabled son and is eligible for a heating grant, however when they came out to survey to install it they told her she had no earth present at her supply and would have to get one installed before they would begin work. As i said I have not seen it yet so whether there is one present and just too high reading I don't know. It is a rural cottage with an overhead supply

I am just looking for some advice as I have not done much work on TT systems and I was wondering if someone would be kind enough to advise me on how to go about it/ best earth rod to install etc

Any help appreciated
 
Actually I'd be using my own skills and knowledge to check the ACTUAL situation before spending any money.

Got a call recently from a rather worried lady saying her house was using her metal garage door as the earth. Sure enough there was 10mm GY running to the garage door, but also a nice fairly recent piece of 16mm GY running into the lecky box!
 

Reply to No Earth? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
388
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
970
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
I'm assuming the cable will have to be cleated well to hold it in place anyway, as a stuffing gland ain't going to hold it tight like a SWA gland...
Replies
10
Views
715
It's not the same scenario, though. Tails more than 3mtrs can be overcome by using a fused switch and rcd board, whether the earthing system is...
2
Replies
18
Views
786

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top