no earths at lights and switches and bonding 6mm rather than 10mm

J

jamesb1

what the general take on this if say you where changing a db and and there was bonding present but not the right size but it satifys test limts ? and also say are changingthe db and some switches dont have a earth but are plastic ? and the same with a light fitting a all plastic fitting ?
 
Best practice is to rewire the lighting circuits..........But if this is not going to happen I have on occasion changed the CU as long as all accessories and luminaires on the affected circuit are class 11. A label is provided at the DB, suitable manufactured labels are available from wholesalers.
This approach is fully in accordance with ESC guidelines, the safety of the installation is improved and as long as the correct cert is provided with all the info there can be no comeback if someone in the future fits a class 1 fitting or switch.
 