Do you agree that we only should be working dead when establishing the Zs for final circuits other than socket outlet circuits? That is, don't use the line, neutral and earth probes of the E/L tester except for Ze and Ipsc. Simply add R1+R2 to Ze.
 
A calculated Zs is only theoretical and can be different from a measured Zs, so IMO Zs should be measured unless it really will be dangerous (eg require dismantling live equipment). You can get ES and BC adaptors for light fittings and putting probes on live FCU terminals is hardly 'dicing with death'.
 
Absolutely not. Always test Zs on all circuits how else would you know your circuit complies with the values for maximum permitted Zs. Calculations do not allow for high impedances through some MCB's, RCD's etc.
 
Health and Safety gone mad these days, if you follow the book then Les you're probably correct...no live testing where possible. However, have to agree with Archy and Adam on this one...a measured Zs is far better on the cert than a theoretical one IMO. I think it is acceptable to add R1+R2+Ze for every circuit if you want, but i personally prefer a measured value when/where possible.
 
I won't answer your question directly because I understand my favourite scam suggest what you say

I will however say that once upon a time Electricians were taught to work with electricty,now make of that statemnt what you will

One clue I will reveal,live working focuses my respect if not any avoidance fears
 
Absolutely not. Always test Zs on all circuits how else would you know your circuit complies with the values for maximum permitted Zs. Calculations do not allow for high impedances through some MCB's, RCD's etc.

Completley agree. I think though, that if your theoretical Zs complies it's fine...which is stupid. Theres an apprentice, that used to do abit with me - now with another sparky i know, and apparantly on the 2395 testing and inspection practical exam they wouldn't allow any live testing of the circuits...all measured, and this was fine by them.
 
I won't name the company but they one company out they that gone Heath and safety madness, your not aloud to test live without signing a folder of paper work
 
I agree with all of you but the local college doesn't advise live testing of Zs, just as Markc123 said above. Is there not a call for say BC adapter leads and small and large and giant ES adapter leads for loop testers? So no H & S inspector walking in on me probing behind a FCU for a Zs reading would be critical? Same at any other live terminals, except at the incoming supply with the main earthing lead disconnected and the CU main switch open?
 

So no H & S inspector walking in
on me probing behind a FCU for a Zs reading would be critical?


If he was to play his silly H+S games whilst I was working live and possibly distracting me in any way,he would soon have my very rigid H+S boot targeted straight up his rear end and would be more concerned with extracting the said rigid boot out of his rear end than being critical of my practices

 
How is testing the incoming supply safer than testing the furthest point of a circuit? The furthest point would be protected by an MCB and RCD, the incomer just by the service fuse.
I suspect the reason for 'having to' test Ze live is because 'there's no other option', which doesn't make it any safer.
 

Reply to No live testing except where it's a must in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Duh!!! Just re-read Op's original post, it was converted to a RFC!
Replies
12
Views
700
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top