Do you agree that we only should be working dead when establishing the Zs for final circuits other than socket outlet circuits? That is, don't use the line, neutral and earth probes of the E/L tester except for Ze and Ipsc. Simply add R1+R2 to Ze.
Discuss No live testing except where it's a must in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Absolutely not. Always test Zs on all circuits how else would you know your circuit complies with the values for maximum permitted Zs. Calculations do not allow for high impedances through some MCB's, RCD's etc.
Re: No live testing except where it's a mustTrying to work out how to do a dead Ze test
lol
......Do you agree that we only should be working dead when establishing the Zs for final circuits other than socket outlet circuits? That is, don't use the line, neutral and earth probes of the E/L tester except for Ze and Ipsc. Simply add R1+R2 to Ze.
So what about Ze, PEFC,PSCC? Or are those live tests acceptable? I've probably never heard such nonsense. Rather than discouraging these tests they should be teaching students how to carry them out safely and properly.I agree with all of you but the local college doesn't advise live testing of Zs
I agree with all of you but the local college doesn't advise live testing of Zs, just as Markc123 said above. Is there not a call for say BC adapter leads and small and large and giant ES adapter leads for loop testers? So no H & S inspector walking in on me probing behind a FCU for a Zs reading would be critical? Same at any other live terminals, except at the incoming supply with the main earthing lead disconnected and the CU main switch open?
In that situation I would argue that if it's so dangerous to test Zs then there's no way you should be testing Ze. If there's no better way to safely isolate and lock off, leaving a suitable sentry by the switch is acceptable IMO.Adam, that's all very well but I was told of a factory inspector or similar reported a spark who was working in a warehouse that had been flooded and left the app standing by at the main dist board as a "safe Isolation". Again if these guys did appear on site you cannot assume you know better even if you think you do. I feel the same as you but have to respect the bofins.