It is a dist board and should have been given circuit protection from day one unless its switch and supply conductors were rated at 200A.
its the same as when you tap of a large busbar with a smaller CSA of cable overload is located on the load side of not more than 3meters.It is a dist board and should have been given circuit protection from day one unless its switch and supply conductors were rated at 200A.
If originally the load profile wasn't going to exceed the rating of the main switch then it would have been acceptable.
In this case then yes it now may not be