Went to view a kitchen refit this week, new kitchen and new rfc circuit dedicated to the kitchen, have a look at the CU and whilst inspecting I see that the 2 lighting circuits, up & down, are both wired with the same 1mm 3&E cable (pre 2005 cable)
Red as line to down mcb, yellow to up mcb, blue to neutral bar and earth to earth bar,
I am relatively new to this game but I’ve never seen that before and the customer says she’s never had any problems with it,ask for any old paper work and the cert (won’t mention the scams name) for a CU change doesn’t mention it but then it also says all IR readings were perfect ha ha!
 
I'm struggling to find anything seriously wrong with this setup. I'm assuming 2 6A SP Mcb's isolating the up and down L circuits. so what we have is a shared Neutral which is not uncommon. So without some rewiring they will both have to be on the same Rcd, which again in not uncommon.

I've seen similar done in the 1960's using singles to a central point which is then split to various circuits. It only means the neutral is joined further down the line rather than joined at the neutral bar.

Regarding safe isolation, without a DP MCB the only way to isolate the neutral is with the main CU switch. This set up doesn't alter that.

So what big problem am I not seeing here?
 
But in a conventional CU without DP Ocpd all the neutrals are shared. Hence the need for a safe isolation procedure.

What some of you seem to be saying is your failure to carry out safe isolation make the installation inherently dangerous?
 
Last edited:
But in a conventional CU without DP Ocpd all the neutrals are shared...
Yes, but no. The N are normally connected at the bar, but current in one circuit does not return to the bar via a different circuit's N (without a fault :)). In the case here, one MCB is off, but the other MCB is putting current into the common N. If you put a tester on that N it may only have millivolts on it at that point, but separate the N and suddenly one end goes to full L via that load.
 
Sumed up very well there Pete each skill set or niece of electrical work has its own set of skills although we are all putting in rings and radial circuits. The problem with these short courses is they may cram in everything academically with a limited practical but it doesn't replace a longer term on the job training. The OP will encounter these problems of existing installations on most occasions this is where experience & training comes in. How do you think the likes of Pete,Tel and even myself got over these issues before all the schemes helplines and internet forums.

simplesss. we blagged it.
 
single pole isolator is fine in TN systems, safe isolation procedure only checks the voltage between all conductors before separating them, no one would be testing for dead every time they separate a conductor. Maybe we should be using clamp meters on every conductor before separating?
To the OP perhaps the only responsible solution if you can't get permission to put on one circuit, would be to put a danger label so at least it's obvious two circuits need isolating before working on the cirsuit.
 

Reply to No pics sorry............ in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
450
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
And exciting when that Hager AFDD finally tripped 😂
2
Replies
28
Views
2K
nicebutdim
N
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top