No RCD !! C2 or C3 | on ElectriciansForums
Discuss No RCD !! C2 or C3 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Manchester
Got an EICR to do tomorrow so just getting a headstart on paperwork .. customers sent me a few pics , straight away fuse board is OAF .. no RCD ... Now .. how do I code this ? And what's your thought process ..
I have it in my head that , should a customer be able to run an extension lead out the door /window of the house and use a Jetwash or any other equipment .. I regard this as "potential danger" C2 ? ...
Most would say C3 and I agree In some respect
.. Napit Codebreakers book is great but not 100% clear on the situation ... Any train of thought would be nice thanks
Potential use of outdoors equipment is a C2. TBH no point chucking codes at it until you've inspected the installation.
No point mincing about these days imo
if it ain’t got any rcd on the installation then i Strongly recommend a board change before even bothering spending 4 hours doing an eicr which ultimately will just fail due to lack of any rcd protection
I personally look at the condition of the installation, if class 1 accessories, electric shower fitted, outside lighting etc its a C2 for me personally. Boards and Installations can be OAF and still be serviceable and safe.
Reply to No RCD !! C2 or C3 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Thanks for the reply littlespark. Yes the works have been carried out. Surely it is fraudulent because basically the document is Not...
I opened up the CU again and the round junction box above and what I found was the blue and brown wires coming in from the wall just above the 15a...
2 3