Hi all,
I got job which client ask me to replace 20 down lights and install new bathroom extractor fan but DB is not RCD protected.(client dose not want change DB )
can I do my job without changing DB or I must change DB?
Thank you
 
Hi all,
I got job which client ask me to replace 20 down lights and install new bathroom extractor fan but DB is not RCD protected.(client dose not want change DB )
can I do my job without changing DB or I must change DB?
Thank you
If your works will involve alterations(adding lights?) You will require additional protection for the lighting as it’s domestic and for the circuits serving the bathroom location. If it’s like for like replacement items then it could be classed as just maintenance and not an alteration or addition to the existing installation.
 
Last edited:
changing lights, like for like, is no problem. if the fan is a replacement, it'sOK . if a new install, then RCD must be added, preferably to all circuits in bathroom. if client refuses, walk away.
 
As soon as it involves adding cable between lights, it’s an alteration, so minor works and rcd required.

Asking the question, as I’m sure we’ve all been in similar situations.... but maybe an enclosure on the outgoing circuit from the Fusebox containing an rcd?
 
Hi all,
I got job which client ask me to replace 20 down lights and install new bathroom extractor fan but DB is not RCD protected.(client dose not want change DB )
can I do my job without changing DB or I must change DB?
Thank you
You will be expected to provide RCD protection for the Bathroom.
 
Do the lights replacements and while you are there cost em up a new rcbo consumer unit and try to sell them on the added benefits of an upgraded fuse board.
if they don’t want the consumer unit you can’t force them and just bill em for the lights
 

Reply to No RCD Protection in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
293
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
802
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
834

Similar threads

Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
2
Replies
17
Views
785
  • Question
I seem to find two types of installation in older houses in which electric showers have been added: those with shower fed from an MCB without RCD...
Replies
9
Views
833
nicebutdim
N

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top