Split ring from a MR DIYER attempting some home electrics, thats what my cash is on
 
nope. he's getting 0.00 ohms. could be his meter resolution is pants below , say 0.4ohms.
 
The Megger multifunction tester i use does this sometimes, turned out the batterys were low in the kit, would just display "0.00ohms" when attempting continuity
 
Correct !, 8 AA buggers too

Luckily the wholesalers always seem to have a offer on batterys, 8 duracell AA's for ÂŁ2
I dont know why im complaining because i dont pay for them, the company does :)
 
Well what a day guys, the job in question is my 1st NIC assessment job in the morning, I took the rfc apart, one leg in MCB tested point to point, powering on and off testing every end each time being very thourgh, and followed it around the house and came back to the disconnected end at the cu. retested and again 0.00 ohms on live and nuetral. tester just been calibrated, zeroed leads, all other circuits turned off. in the end I had to leave it otherwise I would not have finished in time for morning assessment. i took out the 32A MCB and replaced it with a 20A just incase. dont know how its going to affect my assessment in the morning which is a cu change by the way............what you think guys?
 
still got all the paper work to do now aswell..........gonna be a long night, why do I leave things to the last minute.....Grrhhh
 
Unfortunately if you do not have a compliant system it is difficult to complete the paperwork, however one could say that the CU replacement was successful but the circuit in question is faulty and has been disconnected. (pending further investigation!)
With a resistance of a 2.5mm cable being 0.008ohm/m you must have a link fault within 0.5m of the CU as anything above that would likely show as 0.01ohm and not as zero on the meter (depending on the meter resolution). Assuming your batteries are up to spec. in the meter.
Best way to test I would say is to disconnect all the RFC wiring from the CU keep all the ends separate join your meter with a long lead to one of the, say neutral, cables and go round each socket with the meter and test the resistance of that one wire (using a socket adapter); if the resistance is zero all the way round, then there is a problem with your meter, if the resistance increases up to the middle and then decreases as you reach the other end of the ring then the ring is linked close to the meter, if the resistance increases each time you move further away then try starting at the other end of the (in this case neutral) cable if again the resistance increases steadily... Ah bit stuck but you could use the largest value as close to n-n reading (no do not do that, that is wrong) but ring should be OK. Similarly with the line conductor.

Good luck with the assessment, do talk to the assessor and they should be understanding, they normally do want you to pass even if only to get your money!
 
Could you not say to the assessor that the job is WIP, outline the "issues" and steps, taken so far, to find the fault(s) and the "solutions" that you are considering??
 
The test for ring continuity is a 3 step test, not just end to end
You have only identified a closed ring but not a satisfactory ring circuit

Your best bet would be to explain to the assessor that you have carried out the cross connecting ,but the results were as you have described
You have decided to treat the circuit as a radial,the zs maximum is the result you are then interested with

Because you have not tested for ring continuity with the 3 step test,if you tell him that you have carried out only end to end testing, he may be less understanding of you
 
Could be a fault on the meter, try measuring with another meter. I've had this with my Fluke 1650, I checked it against another multi meter and got a reasonable reading.
 
Could be a fault on the meter, try measuring with another meter. I've had this with my Fluke 1650, I checked it against another multi meter and got a reasonable reading.
I apologise if I teaching my mother to suck eggs, but try checking the crock clips. On all the ones I've seen, only one side of the jaw (the fixed side) is connected to the cable, the other jaw (moving side) relies on the connection through the spring. You may have nulled out the leads on one or both of the moving jaws rather than the two fixed jaws together.
 
It's likely as BlueToBits said, you may have nulled out the leads on one or both of the moving jaws (hinged jaws) rather than the two fixed jaws together. If leads aren't nulled properly you will get all sorts of confusing readings.

Also replace the batterries.

Best of luck with your assessment!
 

Reply to no resistance end to end on L & N in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
819
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
897

Similar threads

Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
333
Induced voltage can be a bit of a red herring when using DVM my guess is somethings moist.
Replies
5
Views
436
TerryBNZ
T

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top