Noisy,buzzing contractor
I think the control cables should be closer to the size of the main cables feeding in.
That would be a better practice
Sorry for the disagree red cross Mate, but a main circuit sized conductor for the control circuitry, apart from be unnecessary is impracticable, have you ever tried getting main circuit sized conductors, say above 2.5mm2 cable into the coil/pushbuttons etc terminals?
The control circuit has lower consumption therefor a smaller cable suitably fused down should be employed, sorry for the red cross by the way, if it's a large load say for example fed by 10mm cable are you suggesting using 10mm cable for the control circuit as well
A silly practice I think Steviec 1:
The control circuit has lower consumption therefor a smaller cable suitably fused down should be employed, sorry for the red cross by the way, if it's a large load say for example fed by 10mm cable are you suggesting using 10mm cable for the control circuit as well?
Not at all,imagine f a fault developed at the point where the main cable enters the isolator/contactor. If the main cable is 25mm and the control cable is 2.5mm, there is a danger that the smaller cable could suffer "burn out". This could result in a fire!!
The control feed at this point should ideally be the same or at least 50% of the size of the main cable until it reaches the circuit breaker or fuse for the control circuit.
Of course ideally the cables of dissimilar size could be fed from a busbar system and bolted seperately, this would negate the problem.
Only if the fuse /mcb didn't operate
Agree, usually a ctrl cable supply comes from elsewhere.like a BMS SYSTEM,if not a C.C supply should of been installed @ some point.
Maybe a 10 amp C.C.
Cliffed: If you take a butchers at page A5 of:
https://datasheet.octopart.com/RT1S-General-Electric-datasheet-42641207.pdf
it explains the coding system for the part number of the GE contactor series you are working on. The last few digits refer to the coil voltage. Looking at the image you provided these numbers are 400 on the new contactor. An earlier 'A' in the part number means an ac control circuit.
I suspect you have swapped a defective contactor with a 230V ac 50Hz coil for one with a 400V ac 50Hz coil - this would explain the noise and chattering as the coil struggles to close the contactor against the opening springs. You have already pointed out the control circuit is powered L-N thus 230V ac.
He ought to know better being a Qualified Engineer and all.
The pic is the old contactor,the coil is 230v.
May I ask what the contactor supplies power to? Did it buzz/chatter before? You may want to check all the connections up and downstream of the contactor to see if that makes a difference. A poor or higher resistance connection in one of the lines or neutral will unbalance what would otherwise be a balanced load and thereby create voltage distortion and thence perhaps a distortion of the current through the coil leading to buzzing and noise. Just a thought.
I'd chuck them off site. Last thing you want is someone half-cut snooping around your stuff.
Wait, what? Not a 'nosy boozing contractor?'
In that case IME 95% of all noisy buzzing contactors are mechanically stiff or dirty, not assembled properly or the wrong coil spec. But as Marconi points out, check the coil voltage directly at the terminals in case it's low.
It supplies a TPN DB.