Work to bond the gas yesterday,when i got to the consumer unit,which had recently been changed,there was no sign of the 10mm earth for the water bond,which i was assured was in place....investigation finds 10mm from stop cock outside to an earth rod,and 10mm from stop cock to the gas pipe on a very handy combi boiler which has been supplementary bonded!:confused:
 
Work to bond the gas yesterday,when i got to the consumer unit,which had recently been changed,there was no sign of the 10mm earth for the water bond,which i was assured was in place....investigation finds 10mm from stop cock outside to an earth rod,and 10mm from stop cock to the gas pipe on a very handy combi boiler which has been supplementary bonded!:confused:

542.4.1 In every installation, a main earthing terminal shall be provided to connect the following to the earthing conductor:

The cpc's

The protective bonding conductors

Functional earths

LPC's
 
Yep, wrong wrong wrong. I think you'd be introducing different earth potentials to the place, which is one of the things bonding tries to get rid of.
 

Reply to the thread, titled "Not rite....but how wrong is it ?" which is posted in Australia on Electricians Forums.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Daily, weekly or monthly email

Back
Top