Work to bond the gas yesterday,when i got to the consumer unit,which had recently been changed,there was no sign of the 10mm earth for the water bond,which i was assured was in place....investigation finds 10mm from stop cock outside to an earth rod,and 10mm from stop cock to the gas pipe on a very handy combi boiler which has been supplementary bonded!:confused:
542.4.1 In every installation, a main earthing terminal shall be provided to connect the following to the earthing conductor:
The cpc's
The protective bonding conductors
Functional earths
LPC's
Yep, wrong wrong wrong. I think you'd be introducing different earth potentials to the place, which is one of the things bonding tries to get rid of.