Guest viewing limit reached
Work to bond the gas yesterday,when i got to the consumer unit,which had recently been changed,there was no sign of the 10mm earth for the water bond,which i was assured was in place....investigation finds 10mm from stop cock outside to an earth rod,and 10mm from stop cock to the gas pipe on a very handy combi boiler which has been supplementary bonded!:confused:
542.4.1 In every installation, a main earthing terminal shall be provided to connect the following to the earthing conductor:
The cpc's
The protective bonding conductors
Functional earths
LPC's
Yep, wrong wrong wrong. I think you'd be introducing different earth potentials to the place, which is one of the things bonding tries to get rid of.
DURHAM
If other, please explain
none
Business Name
good earth electrical
Not rite....but how wrong is it ?
Australia
zedess,
zedess,