My 3 year old install for a while has been giving me issue with nuisance tripping the 30ma RCD in a 17a Split board I had originally thought the cause was a faulty outside light but one morning recently it was tripping so many times I managed to isolate the problem by switching of the MCB to the inverter..
This only seems to happen on very wet windy mornings when the Inverter is starting up, having read the manual I also have concerns about the shut down times on the inverter when connected in the way it is at present.
I believe this to be a common problem and my understanding is the best course of action is to move the PV system from the Main CU to a garage unit but what I cannot find for certain what breaker is required.
I have a 16 Panel 4kw system on a Power-one 3.6-TL-outd inverter
All the cabling is surface mount in the roof space or in conduit else where
Any advice you could offer ?