If after doing the necessary testing you find no fault, I suspect the problem to be a high in-rush current when the switch is first made. LED lamps and their drivers do have high but short duration in rush currents and in your case you turn on 4 at the same time.
You could fit one of these:
http://www.cooper-ls.com/sites/coop...eets/cooper-ls-datasheet-inrush-limiter_0.pdf
an inrush current limiter with a rating of 16A.
see also:
ESB AC Inrush Current Limiter 3,6kW ... 48kW CAMTEC Power Supplies - http://www.camtec-powersupplies.com/inrushcurrentprotection_esb.html
You could fit one of these:
http://www.cooper-ls.com/sites/coop...eets/cooper-ls-datasheet-inrush-limiter_0.pdf
an inrush current limiter with a rating of 16A.
see also:
ESB AC Inrush Current Limiter 3,6kW ... 48kW CAMTEC Power Supplies - http://www.camtec-powersupplies.com/inrushcurrentprotection_esb.html