Tested an RCD spur earlier with some odd results

Tested at x 1/2 (both waveforms) and no trip
x 1 (0 degrees = 28.5 ms), (180 degrees = 18.4 ms)
x 5 (0 degrees = 8.2 ms), (180 degrees = 40 ms)

S0 getting bang on 40ms at x5 on 180 waveform; i know its in limit but was expecting it to be (at least) as low as the x5 0 degrees result.

The supply is TNCS, the circuit has low Zs, testing carried out at rcd spur itself, with load side disconnected. Tried it with two different sets of leads and same result, the testers been recently calibrated.

What would you do in this situation ?? I realise the x5 result is within limits (just). Really im perplexed, if this result is due to the nature of the waveform, or if the RCD is iffy.

And to add to the mix im reading that x5 rcd tests are , strictly speaking only required where your max Zs values cannot be met.. e.g. TT installations.
 
Last edited:
Tested an RCD spur earlier with some odd results

Tested at x 1/2 (both waveforms) and no trip
x 1 (0 degrees = 28.5 ms), (180 degrees = 18.4 ms)
x 5 (0 degrees = 8.2 ms), (180 degrees = 40 ms)

S0 getting bang on 40ms at x5 on 180 waveform; i know its in limit but was expecting it to be (at least) as low as the x5 0 degrees result.

The supply is TNCS, the circuit has low Zs, testing carried out at rcd spur itself, at load side with circuit disconnected. Tried it with two different sets of leads and same result, the testers been recently calibrated.

What would you do in this situation ?? I realise the x5 result is within limits (just). Really im perplexed, if this result is due to the nature of the waveform, or if the RCD is iffy.

And to add to the mix im reading that x5 rcd tests are , strictly speaking only required where your max Zs values cannot be met.. e.g. TT installations.
How many times did you carry out the tests? could be just a glitch
 
5x rcd tests on 30mA rcd’s are for the circuits circuits requiring and covered by said rcd and require additional protection so must trip within 40mS @ 150mA regardless of what type of earthing arrangement is in place.
 
5x rcd tests on 30mA rcd’s are for the circuits circuits requiring and covered by said rcd and require additional protection so must trip within 40mS @ 150mA regardless of what type of earthing arrangement is in place.

Yeh additional protection against direct contact , x1 tripping times below 200ms would account for that where the circuit has a low enough ZS would it not ? I know the regs state x5 have to be within 40ms for TN systems too, but thats' backup to protect against a low high Zs scenario aint it
 
Last edited:

Reply to Odd test results on RCD Spur in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
756
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
746

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top