I wonder if anyone can offer advice on storage heating circuit design.

I have a job to replace two BS3036 fuse boards, with 17th Edition consumer units. One of the boards will manage the existing storage heaters for the property, currently three heaters, old & no idea of size but each fed via 15amp fuses and 3kw immersion heater. This board receives an 'Economy 7' supply. The property also has 8.5kw electric shower, fed from the standard supply.

My client wishes to increase the storage heaters from three to six. The property has a 100amp supply. Clearly I will need to calculate the new demand, but even just basing it on 2.5kw heaters and the immersion, that is 64amp approx. If the client uses the shower at the same time as the heaters receive their charge, that is approaching 99amps.

I have already advised my client, but if I install 6 x 16amp circuits, there is potential to overload the DNO fuse.

Never installed an off peak board before, I've considered having a DP MCB as a main switch to prevent overload of the DNO fuse, or is it just case of calculating maximum demand for the normal tariff board and limiting the number of off peak circuits?
 
I know this is a more expensive alternative but you could talk to the customer about the benefits of installing an electric boiler with a wet system. It offers so much more flexibility of heating a home and can provide heat whenever it is needed and/or wanted.

The boiler itself could most likely be installed in the same place the existing cylinder is now.
 

Attachments

  • [ElectriciansForums.net] Off Peak Heating - Circuit Design
    image.jpg
    81.2 KB · Views: 134
Last edited:
I wonder if anyone can offer advice on storage heating circuit design.

I have a job to replace two BS3036 fuse boards, with 17th Edition consumer units. One of the boards will manage the existing storage heaters for the property, currently three heaters, old & no idea of size but each fed via 15amp fuses and 3kw immersion heater. This board receives an 'Economy 7' supply. The property also has 8.5kw electric shower, fed from the standard supply.

My client wishes to increase the storage heaters from three to six. The property has a 100amp supply. Clearly I will need to calculate the new demand, but even just basing it on 2.5kw heaters and the immersion, that is 64amp approx. If the client uses the shower at the same time as the heaters receive their charge, that is approaching 99amps.

I have already advised my client, but if I install 6 x 16amp circuits, there is potential to overload the DNO fuse.

Never installed an off peak board before, I've considered having a DP MCB as a main switch to prevent overload of the DNO fuse, or is it just case of calculating maximum demand for the normal tariff board and limiting the number of off peak circuits?

There not many people who'll have a shower after midnight!
 
Maximum off peak load is normally 80amps
normally 3 sizes of storage heater(bathroom heater can be smaller)
Dimplex heater sizes
small 1.7kw
medium 2.55kw
large 3.4kw
immersion heater 3kw
Ps:- these ratings were the same when 240v was used for calculations
as long as the house has a mixture of sizes of heater then the loading should be ok
 
There not many people who'll have a shower after midnight!

But maybe early morning!

Worth asking what are the chances of all the storage heaters actually being turned on? Let alone on full blast.

As a (slightly long winded) example - I live in a moderately sized 2 bedroom rented flat (spread over one floor) with 2 storage heaters - Hall (XL18) & Lounge (XL24) There is panel heaters in the bedrooms, plinth heater in the kitchen & fan heater in the bedroom. Currently we only have the Lounge one about 2/3 of the way, with leaving the doors open throughout the day it provides enough heat for the entire flat (around 20 deg). Through the winter we had the hall one on too (also being around 2/3 on) this kept the place warm over the worst of the cold no bother. The only time we have used any of the other heating is on the odd night recently when it's been colder stuck the panel heater on in the wee ones room (she won't sleep through if it's not bang on 20deg!).

Think I worked out it costs us about £3 a day to heat the place through the winter (both heaters on with occasional panel heater too).
 

Reply to Off Peak Heating - Circuit Design in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

If two tariffs are sufficient, and you don't need too many ways, you can easily add an SPD kit to the Fusebox F2014DT dual tariff board. The only...
Replies
1
Views
282
  • Question
Part III:). I think I have clarity-having spoken to my electrician who installed my heaters, he said that the part of my fuseboard that is...
2 3 4
Replies
52
Views
2K

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top