What tests and how do you go about commissioning an intruder alarm system due to ohms law.what readings must you look for what resistance levels to check for in tamper circuit alarm circuit, quiescent circuit and how do you commission the PIR's to the CIE and how do you test different wiring like FSL (Eol) wiring or Double Pole wiring. Thanks Ste.
 
measure the loop resistances alarm and tamper. readings will be the resistance of the cables, except with active devices where you will have open circuit on the alarm pair with no power to thre device, and in the region of 10 ohms when powered. with eol resistors, the reading will be the eol resistor if the detector is closed, and both resistors added if the detector is open.
 
92 Ohms per KM on CQR cable. (9.2 Ohms per 100m)

In terms of commissioning tests that require a meter and documenting:
Detection zone resistances per circuit in a quiescent state.
Current draw from each powered device.
Whole system load test current draw in quiescent and alarm.
 

Reply to Ohms law intruder alarms in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
259
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
749
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
738

Similar threads

I have this set: RS PRO Circuit Breaker Finder | RS - https://uk.rs-online.com/web/p/continuity-testers/1938690 and as others have said it takes a...
Replies
7
Views
1K
Thank you, what would be the advice for me to do in this scenario? I've also seen circuits tripped in past from other things such as 1500VA step...
Replies
6
Views
511

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top