Im newly qualified but haven’t come across a house wiring as old as this one and would appreciate any advice you can throw my way,

House is approx. 80 years old and still has original CU fitted, couple (friends) don’t want to start thinking about rewire etc at their stage of life, but my main concern is to make the outside wiring attached safer than I think it is at the moment.
Old style CU with wireable fuse carriers, all carriers are labelled 5 amp but have different fuse wire used depending on circuit. Reason for this was they haven’t changed the carriers in all the years they have lived there and all socket circuits initially ran from 5 amp fuses, they found problems when they started using more modern electric heaters etc years back. thankfully has the savvy to remember to use appropriate fuse wire rather than just fitting 5 amp like the carrier suggests.

Radial Circuit to garage
2.5 cable although in 5amp carrier has 15amp fuse wire used and runs as a radial to firstly a double socket upstairs and then from there runs outside to garage. Approx. 30ft run of cable.
Circuit goes to a very old style wireable fuse carrier with 15 amp fuse wire, from there 2.5mm cable runs to a junction box where 2.5mm is again connected and runs off as another radial to two double sockets. From same junc box 1.5mm cable is also used to run off to two internal lights and a further 3 outside security lights.
So as it stands they have a lighting circuit and a socket circuit attached on same circuit from main CU with an inline 15 amp fuse carrier box and then also protected by a 15 amp in main CU.
My initial idea was to at least install a new garage CU with a 6amp MCB for lighting circuit and a 16amp MCB for the sockets but doubting that now.
yes the outside fuse is lower rating rather than higher thankfully but they are looking at buying a freezer and possible tumble dryer to use in garage and I have concerns that current circuit will cope.
Any advice please would be appreciated
 
OP: Please can we have some pics of the boards and cables, then perhaps we can guide you as to the age, likely faults, things not to disturb etc. while working out a plan of action. FWIW the oldest cable I have in service in an installation is over 100 years old and fine, while some from the 1960s is no good. Glenn is on the money with it depending on the installation's history and a bit of it is just luck as to how long stuff lasts.
 
yep...its all about the environment its in....the times (and the magnetude) of fault/s it has been subjected to....

the levels of loading under normal conditions

installation method...
the list goes on....
 
oh would it now?

i think not....

see as it would have been as a result of your investigations that the insulation `fell apart`...then you would have a duty of care to make a repair....even if only temporary....

as you also have a duty of care to leave the occupants with adequate power for lighting and outlets....

That was what I was getting out you could end up opening a can of worms just by taking off 1 socket :oops: so message to OP is be care full when doing your inspections
 
hi all sorry i gave up checking forum replies as i was getting loads of messages about playing chess etc lol, yes i will sort out some pics of the installation when i go back next

all the best and thanks for all the advice
 

Reply to old style wireable CU in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
295
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
804
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
839

Similar threads

In Theory that’s a good argument but if you will be adding or moving switches or sockets or adding lights you’ll more than likely end up needing a...
Replies
7
Views
457
  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
770

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top