Andy C

-
Joined
Nov 26, 2016
Messages
89
Reaction score
23
Location
Wirral
I have been doing some work for a hedgehog charity so funds have been tight.
I have remedied a number of non conformity items as they want an EICR for the landlord.

I am happy with the general condition of the circuits and readings are all within range. A number of C3s have been given, with one being lack of cable support in ceiling areas.

The shop has two Wylex boards one metalclad and one plastic. Neither has a lid for where the original rewirable fuses were as these have been replaced with MCBs of various types. I intend to replace the fuse carriers that have open pin connections to closed ones. Doing this, will it be sufficient to pass as there will still be no lid/cover on either board.

The boards are in a cupboard that is secure and only authorised staff have access to.

I have considered sourcing new lids but they would still need the cover cutting out so the MCBs would fit.

The final option is replacement DBs but I want to avoid the cost if I can.

Thanks for any replies.
 
I always code these boards if the fuse cover is missing as live parts are accessible to fingers without the use of a tool by partially withdrawing a device or tilting it, try it if you don't believe me. In a domestic where the board is within reach this would be a code 1, in the situation you describe a code 2. I expect others will disagree but ultimately without the cover in place live parts ARE easily accessible. And yes Spin, I know the apparent original function of the cover was to contain molten copper from fuses, but these days access to live parts is more of a danger IMO.
Suitable warning signs/ labelling and access only to competent persons may justify a code 3.
 
Last edited by a moderator:
I have considered sourcing new lids but they would still need the cover cutting out so the MCBs would fit.

The final option is replacement DBs but I want to avoid the cost if I can.
the amount of time I go to customers property's is is always the lids missing or not marked up .
 
I'm afraid charity or not if there is no cover and you have to cut the new cover I would be reccomending a board change, it'll still be your name on the cert if on some off chance someone sticks their hand in, and cutting lids is out of the question for me
 
Maybe there is some confusion over cutting the lid. The fuse cover on the old wylex boards is designed so that the centre part can be removed/knocked out in order to fit the plug in type mcb's, you are still left with a frame which prevents access to live parts,

Only if the lid is the type with a slotted screw and not the thumbscrew type I suppose ?
 
Some great replies thanks guys. Sadly the lids have long since gone and sourcing replacements is proving difficult.
ihave a 6 way cream wylex lid spare.
 
I changed one of the Wylex 3036 the other day, it had a very good condition lid with the thumbscrew - I took that baby home and put it onto my 3036!
That reminds me, I must get a competent electrician around to change that!
Bussmans holiday and all that!
 

Reply to Old Wylex DBs no lids. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
961
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Ah my mistake - apologies. I have something more or less like this wylex unit and the flappy plastic cover has got a broken pin so won't stay one...
Replies
4
Views
275
Why go to the trouble of adding another cable, which I assume would follow the same route as the other ?. Why not upgrade it. It was to try to...
    • Like
Replies
1
Views
187

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top