Thats what I thought but was more concerned with using a single conductor to combine N and Cpc I would have thought could upset an rcd.

Residual current devices (RCD) rely on detecting currents flowing in the earthing conductor by measuring the out of balance currents between phase and neutral conductors. In a TN-C installation, the neutral and earthing conductor are combined, thus making the detection of residual current impossible.

You cannot tell what is a legitimate neutral current, and what is an earth fault current using the PEN, as the earth and neutral combined.
 
Last edited:
In a TN-C installation, the neutral and earthing conductor are combined, thus making the detection of residual current impossible.
I don't think it's helpful to label this installation as a TN-C. I understand that in some ways that is correct, but it is causing confusion.
In a true TN-C system there wouldn't be an N or a CPC for any of the loads, just a PEN. In a true TN-C setup earth faults are indeed impossible to detect using an RCD.
[ElectriciansForums.net] On the fiddle ______________

In this installation, the neutral and earthing of loads are separated. The loads have N connected to the RCD and the CPC connected to the CPC bar. In turn, the CPC bar is connected to the N incomer on the main switch.
Therefore any current flowing through the CPC will not pass back through the RCD and the RCD will trip due to the imbalance.

[ElectriciansForums.net] On the fiddle ______________
Apart from the colour of the wire, I maintain that it is electrically exactly the same as this:
[ElectriciansForums.net] On the fiddle ______________

Discuss!
 
Last edited:
I cant find a ~100a version of the crossover switch in the picture, one that will link straight through L-R and then when turned join L green to R blue as well as L blue to R green. It's easy enough to do in electronics but I guess no-one makes an electric sized version. Sorry for the floppy CAD, turns out windows paint 3D is ----
 

Attachments

  • [ElectriciansForums.net] On the fiddle ______________
    crossover.jpg
    84.3 KB · Views: 12
In a meter the neutral plays no part in the measurement unless its used to power (with the line) any electronics present in the meter .
i have taken single phase meters apart and there is always a solid neutral link with the live sent though a current shunt , the volt drop is then measured over the shunt to calculate amps
 
I cant find a ~100a version of the crossover switch in the picture, one that will link straight through L-R and then when turned join L green to R blue as well as L blue to R green. It's easy enough to do in electronics but I guess no-one makes an electric sized version. Sorry for the floppy CAD, turns out windows paint 3D is ----
A generator cross over switch or a contactor would do what you want.

I don't know how you would switch a 100amp mains using electronics cheaply.

I don't know what you are trying to achieve in your pic, The OPs had his N supply to the meter disconnected, so the meter electronics wouldn't work, as already said a number of times.

Apart from switching colours and Csa it won't do anything to thwart the meter reading.
 
Last edited:
If it was as easy as disconnecting the neutral from the supply of the mainswitch…. And using earth as the return… basically not having anything connected to neutral out of the meter… to stop the meter running…. Everyone would be doing it.

The meters don’t need the neutral to operate… even the old mechanical ones.


Someone comes to read my meter 2 or 3 times a year, even though I fill it in online when asked to.
I’m sure these guys are trained to notice bypasses, strange boxes, smoking nails hammered into the tails….
 

Reply to On the fiddle ______________ in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
362
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
328
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
371

Similar threads

I have just looked at the wiring diagram on line and there are a lot of internal links which if in the wrong terminal could put 230 volt onto...
Replies
10
Views
767
In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
640
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top