Could you try loosening the socket from the wall completely. plug in the microwave and see if it trips, I have had a similar problem in the past and it turned out although the insulation had not been damaged,with the socket screwed back the cables were pressing on he back box and breaking down to inrush load.
 
Could you try loosening the socket from the wall completely. plug in the microwave and see if it trips, I have had a similar problem in the past and it turned out although the insulation had not been damaged,with the socket screwed back the cables were pressing on he back box and breaking down to inrush load.

Should have mentioned, the back box is a 40mm, due to the overboarding of the wall.
 
Just had a phone call, the mystery is solved, his wife has spilt a kettle full of hot water over it, and it fizzed and died, and tripped the RCD, so the microwave is in the bin!
 
Assuming this is a theoretical scenario?

My thoughs are:

The microwave only has sufficient leakage to earth to trip the RCD when it starts to cook so it doesn't show when PAT tested.

The offending socket is nearest to the consumer unit, so it has a lower Zs than the others.

The leakage of the microwave is only just over the operating current of the RCD. Therefore it operates when plugged into the nearest socket as the Zs is low, but the slightly higher Zs at the other sockets is enough to prevent the RCD operating.


I'm not convinced by my answer, as I suspect the fault on the upstair lights is connected, despite it seemingly having been rectified.

As I say, I'm taking this as a theoretical question to test us, rather than a real situation, so I'm assuming you've given us enough details to solve the problem...
 
Assuming this is a theoretical scenario?

My thoughs are:

The microwave only has sufficient leakage to earth to trip the RCD when it starts to cook so it doesn't show when PAT tested.

The offending socket is nearest to the consumer unit, so it has a lower Zs than the others.

The leakage of the microwave is only just over the operating current of the RCD. Therefore it operates when plugged into the nearest socket as the Zs is low, but the slightly higher Zs at the other sockets is enough to prevent the RCD operating.


I'm not convinced by my answer, as I suspect the fault on the upstair lights is connected, despite it seemingly having been rectified.

As I say, I'm taking this as a theoretical question to test us, rather than a real situation, so I'm assuming you've given us enough details to solve the problem...

This all seems to make sense, the socket is the second nearest by about 4 feet from the nearest, and the microwave wasn't tried in that socket, as it is a cupboard for the washing machine. but we will never know now, but it must have been the oven at fault, the new one works fine!
 
This all seems to make sense, the socket is the second nearest by about 4 feet from the nearest, and the microwave wasn't tried in that socket, as it is a cupboard for the washing machine. but we will never know now, but it must have been the oven at fault, the new one works fine!

Take your own microwave to site and see what happens when that is plugged in the same socket?
 
The leakage of the microwave is only just over the operating current of the RCD. Therefore it operates when plugged into the nearest socket as the Zs is low, but the slightly higher Zs at the other sockets is enough to prevent the RCD operating.

I like this but only if the leakage is caused by an N-E fault in the microwave, that is not connected to the plug unless cooking, or lies in a critical band of resistance.

Zs is only going to vary by a fraction of an ohm from socket to socket, but if the source of the leakage is faulty insulation L-E the leakage impedance must be in the order of kilohms to produce a current at the tripping threshold of the RCD. So changing socket will vary the leakage current by tenths or hundredths of one percent, which is too small to produce repeatable behaviour.

If the fault is N-E, it could be low enough to be of the same order of magnitude as the ring cable, yet not cause a trip unless the circuit is loaded. With an N-E fault one would expect the kettle to cause a trip too when plugged in near the microwave, unless the fault were downstream of the cook relay, which would either have to be DP or switch the neutral (we've seen in another thread that some appliances have internal controls that do this).

Microwave ovens produce heavy inrush currents every time the cook relay closes, exactly how heavy depends on the size and design of transformer. For example, the one on my boat would often trip the B10 feeding my shoreline but another of the same wattage didn't (I cured this by installing a soft-start resistance of a few ohms in the TX primary).
It is possible that this inrush being dumped into a rather higher resistance N-E fault might be enough to trip the RCD while other nearby loads (and indeed the steady running current of the oven) would not.

But we'll never know now. :(
 
Last edited:
Just had a phone call, the mystery is solved, his wife has spilt a kettle full of hot water over it, and it fizzed and died, and tripped the RCD, so the microwave is in the bin!
So why did the microwave work fine in other sockets? And why tell us it PAT tested OK?
There are too many red herrings in this scenario.
 

Reply to One for the theorist amongst you........................... in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
527
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
982
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
916

Similar threads

It was >999 on all, tested cables connected and individually, he ce the reason i came on here to ask for ideas
2
Replies
19
Views
835
Exactly. I was going to ask on the earthing once he clears this boiler fault (suspect on internal component). OP mentions oil boiler but makes no...
2
Replies
19
Views
952

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top