Hi,
1. Why did you open the head? You have no right to do so and the older ones can and do go bang. (research arc flash).
2. When you did the the PEFC test did you isolate the installation, disconnect the earth cable from the terminal shown and test at that terminal?
 
Hi,
1. Why did you open the head? You have no right to do so and the older ones can and do go bang. (research arc flash).
2. When you did the the PEFC test did you isolate the installation, disconnect the earth cable from the terminal shown and test at that terminal?

1. I did not open the head - I was not the photographer.
2. Yes I did. To avoid any chance of multiple earth paths.
 
I would go for TN-C-S.
If you look carefully at incoming supply, the concentric cable has only 2 conductors. The centre line conductor and outer stranded neutral. Part of the stranded neutral has been seperated and used to feed the earth terminal. (Effectively creating a link between them) the remaining strands have then been painted black to form the neutral conductor.

So to my eyesight, which is not what it was, it's combined in the service head, therefore TN-C-S.
 
IMG_2950.GIF

I would go for TN-C-S.
If you look carefully at incoming supply, the concentric cable has only 2 conductors. The centre line conductor and outer stranded neutral. Part of the stranded neutral has been seperated and used to feed the earth terminal. (Effectively creating a link between them) the remaining strands have then been painted black to form the neutral conductor.

So to my eyesight, which is not what it was, it's combined in the service head, therefore TN-C-S.
The neutral and cpc are not combined in the service head and are separate split like the picture
 
View attachment 37591

The neutral and cpc are not combined in the service head and are separate split like the picture

Thanks for the picture - that looks very much like the configuration in the image I originally posted. Just to clarify is the consensus still that this is TN-S?

This would align with the observation that the PEFC and PSSC are different.

Thanks again for very helpful insights from the forum.
 

Reply to Opinion on Supply System Type Wanted: TN-S or TN-C-S in the The Welcome Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
389
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
971
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
A bit like saying plumbers makes good electricians. 🥴
Replies
10
Views
2K
  • Question
That was my saying not long ago about TNS to PME system. I would be nice you can ring up the DNO, will the systems being up graded, there is a...
Replies
9
Views
2K

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top