A block of flats has various external lights not just attached to the building but around the grounds. Part of the circuit has twin and earth going underground with good readings but clearly unsuitable cable for external/underground use (not contained in any form of conduit).

The swa on the circuit is 2 core but the steel wire has been cut short on some lights at the top of brick piers with a couple of rusty strands of it attached to terminal blocks to connect to the lights earth, and not surprisingly the steel wire reading as the cpc as good as non existent with silly results (so the cpc is a 100% fail),

There are other ground lights that also have 2 core swa and the steel wire is not earthed (zero reading).

There is also no RCD protection for any external lights.

I am swaying between C1 and C2, so opinions appreciated.
 
Last edited:
A block of flats has various external lights not just attached to the building but around the grounds. Part of the circuit has twin and earth going underground with good readings but clearly unsuitable cable for external/underground use (not contained in any form of conduit).

The swa on the circuit is 2 core but the steel wire has been cut short on some lights at the top of brick piers with a couple of rusty strands of it attached to terminal blocks to connect to the lights earth, and not surprisingly the steel wire reading as the cpc as good as non existent with silly results (so the cpc is a 100% fail),

There are other ground lights that also have 2 core swa and the steel wire is not earthed (zero reading).

There is also no RCD protection for any external lights.

I am swaying between C1 and C2, so opinions appreciated.
Page 165 Blue OSG give a fairy comprehensive guide to EICR codes read and inwardly digest.
 
A block of flats has various external lights not just attached to the building but around the grounds. Part of the circuit has twin and earth going underground with good readings but clearly unsuitable cable for external/underground use (not contained in any form of conduit).

The swa on the circuit is 2 core but the steel wire has been cut short on some lights at the top of brick piers with a couple of rusty strands of it attached to terminal blocks to connect to the lights earth, and not surprisingly the steel wire reading as the cpc as good as non existent with silly results (so the cpc is a 100% fail),

There are other ground lights that also have 2 core swa and the steel wire is not earthed (zero reading).

There is also no RCD protection for any external lights.

I am swaying between C1 and C2, so opinions appreciated.
Page 165 Blue OSG give a fairy comprehensive guide to EICR codes read and inwardly digest.
 
I was under the impression rcd protection on lighting circuit in 18th edition is not just limited to dwellings only.

I've just C3 ed a whare house lighting circuit on an EICR that has no RCD protection as I am carrying out works to the 18th now. Client doesn't have to do anything as it won't give an unsatisfactory.

I will look up reg when get a chance.
 
I was under the impression rcd protection on lighting circuit in 18th edition is not just limited to dwellings only.

I've just C3 ed a whare house lighting circuit on an EICR that has no RCD protection as I am carrying out works to the 18th now. Client doesn't have to do anything as it won't give an unsatisfactory.

I will look up reg when get a chance.
You are carrying out EICRs to the 18th Ed?
 
He’s correct it’s for dwellings
Any circuit supplying luminaries in a dwelling requires additional protection via 30mA rcd

To align with the base CLC Harmonised Document, the new Regulation 411.3.4requires the provision of additional protection by RCD for AC final circuits supplying luminaires within domestic (household) premises.
 
I was under the impression rcd protection on lighting circuit in 18th edition is not just limited to dwellings only.

I've just C3 ed a whare house lighting circuit on an EICR that has no RCD protection as I am carrying out works to the 18th now. Client doesn't have to do anything as it won't give an unsatisfactory.

I will look up reg when get a chance.
Very worrying.
 
Any circuit supplying luminaries in a dwelling requires additional protection via 30mA rcd

To align with the base CLC Harmonised Document, the new Regulation 411.3.4requires the provision of additional protection by RCD for AC final circuits supplying luminaires within domestic (household) premises.
B*gg*r! Yep your correct.
Pleased I haven't sent the EICR yet.
Also really pleased I'm part of forum. Could of been a changer there.
I don't like giving false information to clients, not good for my reputation.

Feel a bit embarrassed now. Why did I think this!
 
Any circuit supplying luminaries in a dwelling requires additional protection via 30mA rcd

To align with the base CLC Harmonised Document, the new Regulation 411.3.4requires the provision of additional protection by RCD for AC final circuits supplying luminaires within domestic (household) premises.

Another stupid regulation.

Why not in commercial premises?
 

Reply to Opinions please EICR code C1 or C2? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
True. Although I'd hazard a guess that things like woodworm treatment are probably chemically quite similar? Don't know.
Replies
13
Views
1K
  • Question
There is no homework, and I'll never see these photo again.
Replies
3
Views
623

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top