Hi guys,
working on a pir yesterday, 2 buildings, readings in main building fine. 10m away there is an out building getting feed from an isolator "in main building" earth reading 50ohms. Can i supply a new earth via a earth rod for the out building and put a rcd on the main switch at the comsumer unit in the out building? the customer had a spark in a couple of weeks ago, he also stated that the high earth and put a rcd before the main switch "in the main building" the problem that i had with this that i was getting high reading and the disconnection time were not begin meet on the mcb's "out building" comsumer unit. the spark said to the customer that under a 100ohms u can put a rcd on it!
any ideas
working on a pir yesterday, 2 buildings, readings in main building fine. 10m away there is an out building getting feed from an isolator "in main building" earth reading 50ohms. Can i supply a new earth via a earth rod for the out building and put a rcd on the main switch at the comsumer unit in the out building? the customer had a spark in a couple of weeks ago, he also stated that the high earth and put a rcd before the main switch "in the main building" the problem that i had with this that i was getting high reading and the disconnection time were not begin meet on the mcb's "out building" comsumer unit. the spark said to the customer that under a 100ohms u can put a rcd on it!