Outbuilding earth rod | on ElectriciansForums
Discuss Outbuilding earth rod in the Australia area at ElectriciansForums.net
T
tomchester999
Hello
I have an outbuilding which has its own earth rod, but I am getting a 280ohm ze.
I have checked the ze in the main building and it is 150.
The earth in the 3 core SWA supplying the outbuilding is not being used, is there any reason or part of the regs that says I can't use the main building earth (rod)
I want to avoid banging in another parrallel rod at all costs as there is a lot of cotswold stone its impossible to get anything in.
thanks
Tom
Ok thank you, I am now getting a reading of 155ohms which is good.
Now, Would i be expected to check continuity of the earth from the main house to the outhouse? (in a run through the tests when you would normally check continuity of main earth)
Is the efli test (ze) enough (for the niceic assessor) as I have never used the stakes in ground method and do not have the kit..
thanks for the help much appreciated
Tom, I would urge you to obtain a copy of Guidance Note 3, all of your points are covered and you can be confident in your testing at your assessment.
Reply to Outbuilding earth rod in the Australia area at ElectriciansForums.net
You would treat it as a TT installation.
I can't help wondering about earthing arrangements and how important aesthetics really are when attempting to make the best of a less than ideal...
nicebutdim
N