Hi all I'm in the process of finishing wiring in outdoor lights.
First thing is there was already lights outside the garage so I replaced these last year and add a light sensor. Which were feed from the lights mcb on the non rcd side of the board. Which have been working. Now I'm installing
2 more and a outside socket in the back garden. And that's where it starts. I understand from the regs that all outdoor lights/sockets to come off the rcd side of the board. So I got another mcb for the lights and sockets to feed from the rcd side wired it all up including the 2 existing on the garage (socket not wired in yet) and it strips the rcd, I've checked all the connections and gone over the circuit several times and is all wired up right. I even made a simple light circuit and that still trips the rcd. But if I wore it to the lighting circuit of the house on the non rcd side it works fine. I understand the rcd has a limit and knowing this I switched off the sockets mcb on rcd side and it still trips the rcd. so I'm at a lose to what the cause of it is any help would be great
 
TL;DR
Outdoor lights trip rcb, but works fine when wired to non rcd side
Possible the circuit you have extended has crossed neutrals with another lighting circuit maybe through the landing two way switching.
 
there will be 2 neutral busbars, one for RCD side and one for the non-RCD side.
Thank you I'll check . I did a electrical course about 18 years ago but never followed it as a career. So I've always checked the regs online when doing and work at home and thank you again if that's it
Possible the circuit you have extended has crossed neutrals with another lighting circuit maybe through the landing two way switching.
Post a pic of the board @Jaco13579 cos it certainly sounds like wrong neutral bar.....one way or another as per @westward10 post ?
I'll post one up tomorrow but guess itthat is the reason as I didnt move the neutral and when i tried the basic lighting circuit i put it in the same place lol
 
Hi all I'm in the process of finishing wiring in outdoor lights.
First thing is there was already lights outside the garage so I replaced these last year and add a light sensor. Which were feed from the lights mcb on the non rcd side of the board. Which have been working. Now I'm installing
2 more and a outside socket in the back garden. And that's where it starts. I understand from the regs that all outdoor lights/sockets to come off the rcd side of the board. So I got another mcb for the lights and sockets to feed from the rcd side wired it all up including the 2 existing on the garage (socket not wired in yet) and it strips the rcd, I've checked all the connections and gone over the circuit several times and is all wired up right. I even made a simple light circuit and that still trips the rcd. But if I wore it to the lighting circuit of the house on the non rcd side it works fine. I understand the rcd has a limit and knowing this I switched off the sockets mcb on rcd side and it still trips the rcd. so I'm at a lose to what the cause of it is any help would be great

like others have said... crossed neutral or quite possibly a fault in some wiring or on the lights you’ve installed being N-E which only trips the RCD. However, the crosses neutral or wrong neutral bar is more likely
[automerge]1595368513[/automerge]
 

Reply to Outdoor lights in the Lighting Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Happy Christmas to everybody
    • Friendly
    • Like
Replies
6
Views
270
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
730
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

Similar threads

Exactly. I was going to ask on the earthing once he clears this boiler fault (suspect on internal component). OP mentions oil boiler but makes no...
2
Replies
19
Views
802
Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top