Hi all I'm in the process of finishing wiring in outdoor lights.
First thing is there was already lights outside the garage so I replaced these last year and add a light sensor. Which were feed from the lights mcb on the non rcd side of the board. Which have been working. Now I'm installing
2 more and a outside socket in the back garden. And that's where it starts. I understand from the regs that all outdoor lights/sockets to come off the rcd side of the board. So I got another mcb for the lights and sockets to feed from the rcd side wired it all up including the 2 existing on the garage (socket not wired in yet) and it strips the rcd, I've checked all the connections and gone over the circuit several times and is all wired up right. I even made a simple light circuit and that still trips the rcd. But if I wore it to the lighting circuit of the house on the non rcd side it works fine. I understand the rcd has a limit and knowing this I switched off the sockets mcb on rcd side and it still trips the rcd. so I'm at a lose to what the cause of it is any help would be great
 
TL;DR
Outdoor lights trip rcb, but works fine when wired to non rcd side
Possible the circuit you have extended has crossed neutrals with another lighting circuit maybe through the landing two way switching.
 
there will be 2 neutral busbars, one for RCD side and one for the non-RCD side.
Thank you I'll check . I did a electrical course about 18 years ago but never followed it as a career. So I've always checked the regs online when doing and work at home and thank you again if that's it
Possible the circuit you have extended has crossed neutrals with another lighting circuit maybe through the landing two way switching.
Post a pic of the board @Jaco13579 cos it certainly sounds like wrong neutral bar.....one way or another as per @westward10 post ?
I'll post one up tomorrow but guess itthat is the reason as I didnt move the neutral and when i tried the basic lighting circuit i put it in the same place lol
 
Hi all I'm in the process of finishing wiring in outdoor lights.
First thing is there was already lights outside the garage so I replaced these last year and add a light sensor. Which were feed from the lights mcb on the non rcd side of the board. Which have been working. Now I'm installing
2 more and a outside socket in the back garden. And that's where it starts. I understand from the regs that all outdoor lights/sockets to come off the rcd side of the board. So I got another mcb for the lights and sockets to feed from the rcd side wired it all up including the 2 existing on the garage (socket not wired in yet) and it strips the rcd, I've checked all the connections and gone over the circuit several times and is all wired up right. I even made a simple light circuit and that still trips the rcd. But if I wore it to the lighting circuit of the house on the non rcd side it works fine. I understand the rcd has a limit and knowing this I switched off the sockets mcb on rcd side and it still trips the rcd. so I'm at a lose to what the cause of it is any help would be great

like others have said... crossed neutral or quite possibly a fault in some wiring or on the lights you’ve installed being N-E which only trips the RCD. However, the crosses neutral or wrong neutral bar is more likely
[automerge]1595368513[/automerge]
 

Reply to Outdoor lights in the Lighting Forum area at ElectriciansForums.net

Similar Threads

Have you notified Building Control of these works?
Replies
19
Views
802
  • Question
As long as the existing wiring is approved for outdoor use and everything is working as planned then there is no need to replace the wiring.
Replies
1
Views
191
In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
488
davesparks
D
SOLVED Thanks for all the help. It was nothing to do with the smoke detector. In this new hole (where there will be a light fitting) three white...
    • Like
Replies
24
Views
3K
  • Question
Or just save all the agro and get a proper sparks round for 45 minutes to test the supply cable and re-fit the socket 'properly'
Replies
19
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks