Hi

I'm just getting myself verified with Elecsa and I'm wiring my 1st job..Just come across a little sticking point!!

Do I wire an outdoor security light off my lighting circuit or do I take it from a FCU spurred off the power circuit?

The only reason I ask is that I always see security lights on spurs, could this be because they were added later?

Cheers
 
you can do it either way to comply with regs. however, i always ( if possible) feed from a 2 pole FCU. then if there's a fault on the outside ( maybe by water ingress) it can easily be isolated by the client, thus allowing RCD/MCB to be reset.
 
If it's a higher power light, such as a 500W flood taking just over 2A, then you might put it on the power circuit rather than overloading the lighting circuit. You need to check what the existing loading on the circuit is and choose accordingly.
 
If you can do it that would be a better way, think about how you can run the cables, which certificate you need to issue etc.
Is the mains up to standard ? have you got enough money in the job etc

Martin
 

Reply to Outdoor security light in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
395
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
986
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
As long as the existing wiring is approved for outdoor use and everything is working as planned then there is no need to replace the wiring.
Replies
1
Views
272
No to all. Also would require a means of isolation for PIV - pulling a fuse wouldn't be acceptable. I don't mean to seem disrespectful, but this...
Replies
1
Views
1K
nicebutdim
N

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top