Hi All,
I was wondering if anyone could help me with a recent problem I’ve had on a job. About 5 months ago I installed about 5 outdoor soffit lights from switch inside. All worked perfectly and customer was happy. I’ve recently been called back to the job as the outdoor lights have been tripping the RCD. I have carried out all Insulation Resistance tests on all legs of the circuits as well as continuity and they all test perfect however it is whenever the switch live twin and earth cable is live even without the load connected it trips the RCD. I have run a temporary cable from the switch to first light bypassing what I believe to be the faulty switch live cable and it all works with no tripping. I know that sort of answers my own question but I am a bit baffled as to how the cable from switch to first light can test perfectly however clearly isn’t . Sorry for the length of this and any help on clearing this up would be massively appreciated, really bugging me , thank you
 
Thanks for replies. I have tested cable from fuse board to switch ( Insulation resistance and r1 + r2, r1 + rn) and is all perfect and then from switch to first lighting point in Wagos and tests perfect however the rcd will stay on with just the feed cable live but as soon as switch live cable goes in without the load connected it is tripping it. I have bypassed the switch with Wagos and there is no damage to any cables at switch point. I’m puzzled because surely if cable was damp at all it would show on IR Test. Im going to have to get another cable out there I think just really baffles me. Perhaps if something has slightly nicked the live conductor somewhere or the neutral and is not causing it to go down the cpc or neutral perhaps it still causes the imbalance therefore tripping RCD ? Thanks everyone for your help
 
Hi - any chance that switched L has been joined somewhere? If you can bypass the cable and it removes the trip and if the cable is not faulty, then I’m thinking some other load has been connected to it and is returning using a different N, which then trips the RCD.
That’s good thinking , cable was run direct and the only bit of work since has been air con unit screwed back on wall however not really where cable was run . Would a Nick in live conductor but not crossing to cpc or neutral have the potential to create enough of an inbalance to trip the RCD. Although I can clearly see a new cable will fix the problem my mind won’t really rest now lol ???
 
when the IR test is being done was the CPC still connected (continuously) back to the CU ? You could have leakage from L or N through the building fabric to true earth, this wont be picked up if IR test is done on S/L CPC at switch position if the CPC is disconnected. And could be only evident now due to the weather
 
when the IR test is being done was the CPC still connected (continuously) back to the CU ? You could have leakage from L or N through the building fabric to true earth, this wont be picked up if IR test is done on S/L CPC at switch position if the CPC is disconnected. And could be only evident now due to the weather
thank you both , this actually seems like it could be the answer as the soffit is aluminium itself and forms part of the metal roof structure ... perhaps somewhere somehow this is the problem ? thanks
 

Reply to Outside Lights trip RCD in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Have you notified Building Control of these works?
2
Replies
19
Views
966
Ok I’ll try this when I’m down
Replies
4
Views
398

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top